Generac 4000XL No Output

I made the mistake last summer of starting my generator with a load applied{plugged into trailer}and the genertor stopped working. The engine starts and runs fine but has no AC output. Does anybody have any idea what may have failed? Was told it might be a failed voltage regulator...?

 
Sponsored Links
30yearTech's Avatar
Member

Join Date: Oct 2006
Posts: 1,176
TX

01-11-09, 07:26 PM   #2  
Have you checked the circuit breakers?? Perhaps they just tripped and need to be reset.

 
carlhunts4fun's Avatar
Member

Join Date: Jan 2009
Posts: 3

01-11-09, 08:01 PM   #3  
Yes all circuit breakers are in order,thanks for the reply

 
Airman's Avatar
Member

Join Date: Feb 2008
Posts: 755
TN

01-12-09, 06:30 AM   #4  
Go to the link below and follow the procedure. You may get lucky is if loss of field magnatism is the problem.

Good luck

PER Notebook - Generator Field Flashing

 
carlhunts4fun's Avatar
Member

Join Date: Jan 2009
Posts: 3

01-12-09, 07:34 PM   #5  
I tried the drill procedure and was unsuccessful. Still no output. I will order a new voltage regulator and let you folks know if that fixes it. Thands again for your response.

 