No Power Coming Out of Generator - Engine Fine

Reply

  #1  
Old 11-24-14, 03:56 PM
Member
Thread Starter
Join Date: Nov 2014
Posts: 5
No Power Coming Out of Generator - Engine Fine

Hi -

I have a Briggs and Stratton Storm Responder 5500 watt generator. Engine runs perfect, but I'm not getting any power to the outlets.

So far I have tried flashing the field using a power drill, but no luck. There is a small LED that lights up the panel. It turns on when you turn the circuit breaker on, and when I ran the drill, the light got much brighter every time I turned the chuck backwards.

I then went to test to see if there was any voltage going to the AVR, but turns out this unit did not have one.

I don't know what to do. Trying to fix it myself if I can. Any help would be appreciated!

Best,
Generator Jimmy
 
Sponsored Links
  #2  
Old 11-24-14, 09:01 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 45,128
Welcome to the forums.

A model number would be a very helpful first step. With that we should be able to dig up a service manual or at least a schematic of your unit.
 
  #3  
Old 11-25-14, 11:34 AM
Member
Thread Starter
Join Date: Nov 2014
Posts: 5
Thanks PJmax. Here you go: Model: 030430
 
  #4  
Old 11-25-14, 11:28 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
Are your connections tight? That's the next thing I would check. Also take the circuit breaker out and check it's continuity.
 
  #5  
Old 11-26-14, 06:33 AM
Member
Thread Starter
Join Date: Nov 2014
Posts: 5
Thanks. I'll try checking the circuit breaker. I'll need to figure out how to check the continuity though.
 
  #6  
Old 12-01-14, 08:04 AM
Member
Thread Starter
Join Date: Nov 2014
Posts: 5
Circuit breaker was fine. Also removed the brushes and it seemed fine, but not really sure how to diagnose faulty brushes. I think I've reached the end of my ability to fix this. Thank you for the replies.
 
  #7  
Old 12-01-14, 05:26 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 45,128
There are two wiring diagrams at the bottom of the six listed breakdown pictures. The wiring diagrams show the generator windings that would need to be checked.

Illustrated Parts List (6)
 
  #8  
Old 12-04-14, 06:43 AM
Member
Join Date: Mar 2009
Location: USA
Posts: 628
Try flashing it. There are u tube videos about, but as I recall, you put a 9 volt battery across one of the110 volt receptacles for an instant as it is running. Be careful, wear eye protection.
Sid
 
  #9  
Old 12-12-14, 06:59 AM
Member
Thread Starter
Join Date: Nov 2014
Posts: 5
Thanks all for your help. Got it fixed. Looks like something in the brush unit was bad.
 