Electric water heater--driving me nuts!

I have 4 year old, 40-gallon, electric water heater at a cottage that I rent. The cottage get used about 5 months a year. The house draws its water from a beach/crock well 30 feet from Lake Huron.

My problem..The heater works perfect if it is in active use: say, 4 showers during a 4 hour period, etc. However, it appears that if it is not in active use for any extended period of time, say, overnight, the water heater does something (???) to trip the circuit breaker. This, naturally, shuts down the unit and one wakes up to an unexpected very cold shower in the morning.

To remedy the situation, I merely reset the breakers and, after a 1 hour wait, will have hot water again, only to do the same thing if the unit is not used heavily during the next hours.
Also, the unit does make noise inside the tank once the juice is turned back on.

Any suggestions would be greatly appreciated.
 
Sponsored Links
  #2  
Old 10-03-03, 08:13 AM
Rainbird's Avatar
Member
Join Date: Aug 2003
Location: California
Posts: 373
Received 0 Votes on 0 Posts
This question might be better addressed in the "Electrical" forum. There might be an electrical safety issue here!
 
  #3  
Old 10-03-03, 08:56 AM
Member
Thread Starter
Join Date: Oct 2003
Location: usa
Posts: 56
Received 0 Votes on 0 Posts
thanks

did post there as well..still if anyone might have a solution, please post

thanks
 
  #4  
Old 10-03-03, 09:12 AM
Rainbird's Avatar
Member
Join Date: Aug 2003
Location: California
Posts: 373
Received 0 Votes on 0 Posts
I see your other posting, it is in "Electric Appliances". You should really put it in the "Electrical" forum. All the Electricians hang out there.

Good Luck...
 
  #5  
Old 10-03-03, 09:24 AM
Member
Thread Starter
Join Date: Oct 2003
Location: usa
Posts: 56
Received 0 Votes on 0 Posts
thanks again


my bad
 
  #6  
Old 10-03-03, 04:24 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,389
Received 0 Votes on 0 Posts
Lightbulb water heater

You didn't say if you did ring out both the elements. just sounds like the bottom element is shot. So when you first turn it on the top one comes on and makes hot water. After your done and it get hot the bottom one turns on Ill bet that thats is when it pops the breaker. Put a new element in the bottom and it will work fine ED
 
  #7  
Old 10-04-03, 04:33 AM
Mike Swearingen's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 1999
Location: Northeastern NC On The Albemarle Sound
Posts: 10,952
Received 0 Votes on 0 Posts
Cool

You either have a bad element or a bad thermostat.
When I have to replace one, I always replace both the top and bottom elements or both tstats.
You can do a Search above for the how-to, or just come back and ask.
Good Luck!
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: