Do I need to ground my copper pipes?
The electrical system in my house is not grounded to the copper tubing. All the outlets, lights, etc, are grounded with a ground wire back to the electrical panel. Do I still need to ground my copper water supply lines? I get water from a rural water supply, but there is a plastic tube coming into the house. I wondered if the copper has some transient voltage that grounding helps with?
Thanks
Chris
Thanks
Chris
#3
Forum Topic Moderator
Originally Posted by majakdragon
Leave the electrical the way it is. Many areas now prohibit grounding to the plumbing system. Most require a ground rod outside the house.
As you said, you certainly need a ground rod (or rods - two are usually recommended) as an underground water main can not replace the house's ground rod.
-Mike
#4
Member
Join Date: Nov 2005
Posts: 236
Upvotes: 0
Received 0 Upvotes
on
0 Posts
At one time it was common pratice to use the water system for THE ground if the connection could be made near the meter base. This was OK in the 60's at least where I lived. You cant do THAT now
Makes sense that they should be bonded because there will be the connections through things like water heater, garbage disposals, and well pumps any way. Check with local code on this but I am pretty sure the restriction Majak mentioned is in using the water system as the sole ground.
Makes sense that they should be bonded because there will be the connections through things like water heater, garbage disposals, and well pumps any way. Check with local code on this but I am pretty sure the restriction Majak mentioned is in using the water system as the sole ground.
#5
NEC 250.104 (A)(1) requires bonding of the water piping system to the equip serv enclosure, the grounded conductor at the service, the grounding electrodeconductor if of sufficient size, or to one or more of the grounding electrodes used.
While this is the NEC, each individual jurisdiction is allowed to make their own rules.
If the area accepts the NEC as their code, then it is required that it be bonded to one of the electrical service bonding/grounding points unless excepted out of their local code.
While this is the NEC, each individual jurisdiction is allowed to make their own rules.
If the area accepts the NEC as their code, then it is required that it be bonded to one of the electrical service bonding/grounding points unless excepted out of their local code.
#6
Member
Thread Starter
Join Date: Nov 2005
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks guys. I think I may have conveyed the problem improperly. Currently my electrical is NOT grounded to the water system. My electrical system has its own grounds. I am wondering though if I need to ground the copper water pipes as they are not grounded since I have a plastic pipe coming in from the rural water. I was wondering if I can just connect a ground from a close circuit to the pipes for this or if something else it needed. Maybe I don't need to do anything.
Thanks
Chris
Thanks
Chris
#7
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
In this situation the proper term is BOND (not "ground") the pipes.
Unless otherwise required by your LOCAL code the hot, cold, sewer (if metal) and gas lines along with HVAC metal ducts should all be bonded to the electrical grounding electrode conductor as close to the grounding electrode as possible.
Unless otherwise required by your LOCAL code the hot, cold, sewer (if metal) and gas lines along with HVAC metal ducts should all be bonded to the electrical grounding electrode conductor as close to the grounding electrode as possible.
#8
Originally Posted by Chris611
Thanks guys. I think I may have conveyed the problem improperly. Currently my electrical is NOT grounded to the water system. My electrical system has its own grounds. I am wondering though if I need to ground the copper water pipes as they are not grounded since I have a plastic pipe coming in from the rural water. I was wondering if I can just connect a ground from a close circuit to the pipes for this or if something else it needed. Maybe I don't need to do anything.
Thanks
Chris
Thanks
Chris
My post states that you need to bond the piping
1. at the electrical service enclosure (service disconnect panel); or;
2.the grounded (neutral) conductor at the panel;or;
3.to the grounding electrode conducor if of sufficient size.; or;
(a GEC is often to do this IF the GEC only connects to the ground rods. There is a requirement per NEC for a particular size conductor (wire) depending upon what is being connected and the service size (amperage) the "close circuit will absolutely not be of the correct size
4.to one or more of the grounding electrodes
So, unless there is a local code that allows you to NOT do this, you HAVE to do it.
As well, furd's post is correct that you have to bond any and all of the systems he posted.