Two bathroom exhaust fans

Reply

  #1  
Old 01-04-08, 06:08 PM
Member
Thread Starter
Join Date: Mar 2006
Posts: 45
Received 0 Votes on 0 Posts
Two bathroom exhaust fans

I have a first floor bathroom that the vent goes into an unheated/only accessible through a removable panel porch roof. I'm guessing this isn't the best plan as there is nowhere for the vented air to go and the added moisture is probably terrible for the roof and such.

I also have a bathroom on the second floor that has no exhaust vent at all. I would like to add a vent to the second floor as well as run the first floor up that direction.

Is there some way to only have one vent for both fans exiting the house? The bathrooms are directly above and below each other. Or do I have to have two separate vents, one for each fan?

Thanks for your help.

Brad
 
Sponsored Links
  #2  
Old 01-04-08, 07:00 PM
Banned. Rule And/Or Policy Violation
Join Date: Dec 2007
Location: Chicago
Posts: 1,011
Received 0 Votes on 0 Posts
M1506.2 Recirculation of air. Exhaust air from bathrooms and toilet rooms shall not be recirculated within a residence or to another dwelling unit and shall be exhausted directly to the outdoors...

If two fans are positively pressurizing exhaust ducts ahead of a common junction to an exterior discharge, then you are recirculating the air from one fan's interior location to the other (less positively pressurized) fan's location.

What you can do is put an in-line fan (like the FanTech products) down-stream of the junction, where it negativitly pressurizes both interior locations, there are both upsides and downsides to doing so.

.. Exhaust air from bathrooms and toilet rooms shall not discharge into an attic, crawl space or other areas inside the building.
 
  #3  
Old 01-04-08, 07:01 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,967
Received 2 Votes on 2 Posts
Brad: you should have separate vents for the two fans, due to the volume restrictions of a single exhaust hose. In other words, if both fans were running at the same time the single pipe couldn't handle the volume of air.
 
  #4  
Old 01-05-08, 09:22 AM
Gunguy45's Avatar
Super Moderator
Join Date: Dec 2007
Location: USA
Posts: 21,107
Received 0 Votes on 0 Posts
Bath fans

Hey Brad,

I get the feeling you really don't want 2 vents for whatever reason.

Depending on your usage patterns, I think you could use one vent for 2 fans, but you would probably have to upsize the vent and vent pipe at the point the 2 fans join. Use a Y pipe to connect the 2 fans, (those are prob 4" outlets) then run a 6" off the Y (of course the 2 legs would be inlets , and the single would be output). I would also install buttterfly dampers on each leg of the fan exhaust, to prevent backflow to the other bathroom, and cut down on drafting.

This would be costlier than 2 vents, if you buy the parts at a big box or hardware store. If you go to a HVAC wholesaler, you will be amazed at how much cheaper the parts would be. Prob less than half the box store cost.

EX: went to a box looking for an 7" adj 90 in galv steel, all they had was cheap aluminum for over $7, the HVAC supplier had just what i wanted, for $2.87!!! wow!
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: