Hi all,

Quick and easy question for you. I am designing the plumbing system for a small remodel and cannot find drainage unit values for a Washing machine.

I have a sink, shower and washing machine sharing a vent pipe. Each will have 1 1/2 inch lines to where they all connect together, but can I get away with 1 1/2 inch all the way to the main vent stack?

The main connection is only about 12 feet away (5 vertical, 7 Horizontal).

Thanks

(toilet is on a separate vent)
 
  #2  
Old 01-05-09, 11:55 PM
steve_gro's Avatar
Member
Join Date: Jan 2004
Location: San Francisco
Posts: 967
Upvotes: 0
Received 1 Upvote on 1 Post
Those vents would tie together into a 2", and 42" or more above the floor.
 
  #3  
Old 01-06-09, 03:59 AM
plumbingods's Avatar
Member
Join Date: Apr 2008
Location: Manch-vegas, New Hampshire
Posts: 1,985
Upvotes: 0
Received 0 Upvotes on 0 Posts
Hi Justin,

According to my info, which is IPC 2006, you will need a 2" drain for those 3 items with a total of 5 DFU's. (w/m = 2 dfu's) with a minimum vent of 1 1/2".
All vents must be a minimum of 1/2 the diameter of the drain it serves.

Remember, I do not know the code book you go by, so if you are unsure, call your local town building official.
 
  #4  
Old 01-08-09, 10:08 PM
steve_gro's Avatar
Member
Join Date: Jan 2004
Location: San Francisco
Posts: 967
Upvotes: 0
Received 1 Upvote on 1 Post
Oops, Plumbing gods is correct (and I was incorrect). UPC allows 8 FU on an 1½" vent. The 42" tie-in point, however, was correct.
 
 