Unvented Shower drain length question

Reply

  #1  
Old 08-12-10, 05:42 AM
Member
Thread Starter
Join Date: Aug 2010
Location: USA
Posts: 55
Unvented Shower drain length question

I figure now is better than later to know if my plan is flawed.

I am putting in a new shower and the planned drain has about a 48" unvented run to the vented waste using all 2" ABS. Dimensions of the layout will be apprx a 8" drop to the P-trap and a 42" horizontal run to a long turn wye.
If I read the code correctly, 2" is good for a combined 60".
The drain should vent itself for this length, correct?

Am I good with this, or am I missing something?

Thanks for any advice.
 
Sponsored Links
  #2  
Old 08-12-10, 11:52 AM
shacko's Avatar
Member
Join Date: Aug 2005
Location: Baltimore County Maryland
Posts: 2,138
If there are above fixtures connecting to the pipe you are tying into you can't do it.
 
  #3  
Old 08-12-10, 12:49 PM
Member
Thread Starter
Join Date: Aug 2010
Location: USA
Posts: 55
Thanks shacko,

The shower is the furthest upstream on a secondary line (vent). Downstream of the wye is the tub. These are the only 2 fixtures on the run. OK now?
 