Moving 2" washer vent this


  #1  
Old 11-13-10, 10:14 AM
D
Member
Thread Starter
Join Date: Sep 2004
Location: So Cal
Posts: 123
Upvotes: 0
Received 0 Upvotes on 0 Posts
Moving 2" washer vent this

My 2" ABS washer vent pipe is right in the way of a new door I am installing up stairs above the washer/dryer space.

I would like to move the vent on the other side of the 2x4 stud and then come back into the original space so I don't need to change the roof exist.

My concern is drilling thru the studs for the vent pipe. If I use 45 degree fittings, the hole thru the stud would seem too large.

What is the correct way to do this?

TIA
 
  #2  
Old 11-13-10, 10:45 AM
D
Member
Thread Starter
Join Date: Sep 2004
Location: So Cal
Posts: 123
Upvotes: 0
Received 0 Upvotes on 0 Posts
Correction:

The vent pipe is 1 1/2" not 2".
 
  #3  
Old 11-13-10, 11:47 AM
shacko's Avatar
Member
Join Date: Aug 2005
Location: Baltimore County Maryland
Posts: 2,002
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by Dan Thompson
My 2" ABS washer vent pipe is right in the way of a new door I am installing up stairs above the washer/dryer space.

I would like to move the vent on the other side of the 2x4 stud and then come back into the original space so I don't need to change the roof exist.

My concern is drilling thru the studs for the vent pipe. If I use 45 degree fittings, the hole thru the stud would seem too large.

What is the correct way to do this?

TIA
If you are at least 42in. above the top of the washer you can use anything you want to offset the vent; always use the least angle that will work.
 
 