capacity of natural gas line
#1
Member
Thread Starter
Join Date: Aug 2008
Location: USA
Posts: 30
Upvotes: 0
Received 0 Upvotes
on
0 Posts
capacity of natural gas line
The gas meter outlet is 1-1/4". One side of a 'T' branches to 3/4" 50 ft. supply to gas furnace (122k BTU). The other side of the 1-1/4" T is blanked off (previously used for swimming pool heater). I don't know how much pressure is on the outlet of the regulator, it's a Rockwell 107 and might be about 45 yrs old.
When my kitchen was remodeled last year, I bought a large 6 burner gas stove (102k btu). The sub-contracted plumber added a 3/4" 'T' close to where the 3/4" heater supply pipe originates and ran a new 3/4" 50 ft supply for the stove.
meter --> 1.25" T --> one side reduced to 3/4" --> 3/4" T --> furnace line & stove line.
So both the furnace and stove supply lines take their gas supply from the same short 3/4" nipple off of the 1-1/4" 'T' at the meter. It seems to me that this may be too much load for 2 high demand appliances and that each of these 3/4" supply lines should run separately from the 1-1/4" 'T' rather than from a 3/4" T. Individually, each line is sufficient according to a table I found on the web. But since they both originate from the same 3/4" nipple off of the 1-1/4" T I'm wondering if this design is under sized.
Should I have the lines redone so that they each branch off from the 1-1/4" outlet?
Or because the supply lines for the 2 appliances branch off only a short distance beyond the 1-1/4" line is the design sufficient? I don't notice any problem in the use of the appliances but I also don't know how to determine if the supply is adequate or not.
thanks, Jon
When my kitchen was remodeled last year, I bought a large 6 burner gas stove (102k btu). The sub-contracted plumber added a 3/4" 'T' close to where the 3/4" heater supply pipe originates and ran a new 3/4" 50 ft supply for the stove.
meter --> 1.25" T --> one side reduced to 3/4" --> 3/4" T --> furnace line & stove line.
So both the furnace and stove supply lines take their gas supply from the same short 3/4" nipple off of the 1-1/4" 'T' at the meter. It seems to me that this may be too much load for 2 high demand appliances and that each of these 3/4" supply lines should run separately from the 1-1/4" 'T' rather than from a 3/4" T. Individually, each line is sufficient according to a table I found on the web. But since they both originate from the same 3/4" nipple off of the 1-1/4" T I'm wondering if this design is under sized.
Should I have the lines redone so that they each branch off from the 1-1/4" outlet?
Or because the supply lines for the 2 appliances branch off only a short distance beyond the 1-1/4" line is the design sufficient? I don't notice any problem in the use of the appliances but I also don't know how to determine if the supply is adequate or not.
thanks, Jon
#3
How far is the total developed length of the farthest appliance?
Furnace or stove?
Example if the stove is the furthest how many ft of 3/4"?
The 3/4" by itself can only supply 151,000 BTU @ 50ft. Now a appliance was added to it.
This is based on .60 specific gravity gas, .5 psi or less, and a .5 inch water column pressure drop.
Most likely you need to change the 3/4 to 1"
Mike NJ.
Furnace or stove?
Example if the stove is the furthest how many ft of 3/4"?
The 3/4" by itself can only supply 151,000 BTU @ 50ft. Now a appliance was added to it.
This is based on .60 specific gravity gas, .5 psi or less, and a .5 inch water column pressure drop.
Most likely you need to change the 3/4 to 1"
Mike NJ.
#4
Member
Thread Starter
Join Date: Aug 2008
Location: USA
Posts: 30
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Lawrosa:
Your questions are the crux of my query.
Each appliance is at the end of s separate 3/4" run of 50 ft (give or take a few feet).
My concern is that they are both fed from a 3/4" 'T' off of a 1-1/4" line and in my mind that reduces the flow to both appliances. Since both appliances are high volume consumers I am afraid I'm starving them. I'm trying to confirm if my concern is correct.
Jon
Your questions are the crux of my query.
Each appliance is at the end of s separate 3/4" run of 50 ft (give or take a few feet).
My concern is that they are both fed from a 3/4" 'T' off of a 1-1/4" line and in my mind that reduces the flow to both appliances. Since both appliances are high volume consumers I am afraid I'm starving them. I'm trying to confirm if my concern is correct.
Jon
#5
My concern is that they are both fed from a 3/4" 'T' off of a 1-1/4" line
If you measure from the meter outlet both appiances are 50 FT?
Mike NJ
#6
Member
Thread Starter
Join Date: Aug 2008
Location: USA
Posts: 30
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The T is right off the meter. Only 3/4" pipe enters the home. The total run of each of the pipes is 50 ft. They were not installed at the same time. When I had a new stove installed (108k BTU) the contractor ran a new line to the stove. The other line goes to the furnace (122k BTU). Both of these lines are 3/4 and start within a few inches of the meter.
jon
jon