Gas line sizing?

I need to run a natural gas line from my meter to the back of my house to install a dryer. The total length of the run will be 90 feet. What size of pipe do I need to put in?
Please disregard, I have found the answer by surfing the web.
 

Last edited by DaleC.; 10-21-11 at 10:35 AM.
Sponsored Links
  #2  
Old 10-21-11, 10:38 AM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 17,722
Likes Received: 2
Hi,

How many BTU is the dryer?

@ 90 ft

1/4 = 10k btu
3/8 = 22 k btu
1/2 = 40 k btu

Should not be more then 38K.

But possibly you want to add to it like a grill.

@ 90 ft

3/4 = 84k btu
1 = 160k btu

Hope this helps.

Mike NJ
 
  #3  
Old 10-21-11, 12:20 PM
DaleC.'s Avatar
Member
Thread Starter
Join Date: Sep 2011
Location: United States
Posts: 9
dry is 20,000 btu. What I found on the web says to use 1/2" for a 90ft. run. 3/8" would be a lot lighter to run. I am planning on exterior run just below the overhang on stucco siding.

Thanks for your reply.
 
  #4  
Old 10-21-11, 01:04 PM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,407
Likes Received: 2
Did you account for the effective length of all the fittings AND for any other usage off of this piping?
 
  #5  
Old 10-21-11, 01:32 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 17,722
Likes Received: 2
As Furd suggests you should run 1/2".

Mike NJ.
 
  #6  
Old 10-21-11, 06:57 PM
DaleC.'s Avatar
Member
Thread Starter
Join Date: Sep 2011
Location: United States
Posts: 9
This will be a dedicated run from the meter to the dryer. Nothing else will be attached.
 