gas piping

Hi,
I am adding an addition on to my home approx 1900 sqft. the existing gas line starts off at 1" the reduces down 1/2" for 75k btu hot air furnace then continues 3/4" to stove/oven (1" x 3/4 x 1/2 Tee). i am adding on when addition is finished to the new boiler and hot water heater being the new furthest point and the total run will be 80'. If I follow the chart correctly I should up the pipe to 1 1/4" or am i looking at this wrong? if i calculated right i have 360cfh. 1 1/4" gas pipe for 80' = 350Cfh which the chart was given to me by the Twp.

Once addition is done:

New boiler 127k @ 80' furthest point
New hot water htr 40k 50 gal at same in boiler room 80'
Stove/oven 83k @ 28'
Exixting furnace 75k @ 13'

Eventually i am going to remove the 75k hot air furnace and add the 4th zone for baseboard to the existing structure but until that is done both units may be running at that same time. I have no problem removing existing and upgrading to 1 1/4" gas pipe a bit pricey but rather be safe and do it right. or can i continue with the 1" pipe to the furthest point the branch off with the other appliances, and do i have to request a new meter with and output of 1 1/4 or can a remove the old 1" and put 1 x 1 1/4" coupling.
 
Sponsored Links
  #2  
Old 06-10-13, 03:35 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 18,138
Received 55 Votes on 48 Posts
I will have to pull out my chart.... ( be back in a few.)

But,

New boiler 127k
That boil will heat a 5k sq ft house... Is the home that big? Did you do a heat loss calc?

Just wondering do you do not oversize. Read the stickys at the top of this forum for heatloss calc.


and do i have to request a new meter
Go out and look at the meter rating plate. Whats the max btu say?

. I have no problem removing existing and upgrading to 1 1/4" gas pipe a bit pricey but rather be safe and do it right.

IMO you may be better off using trac pipe..... ( Must be certified though)
 
  #3  
Old 06-10-13, 04:15 PM
U
Member
Thread Starter
Join Date: Jun 2013
Location: USA
Posts: 6
Received 0 Votes on 0 Posts
Yes did a heat loss heat gain and to be quite honest not sure how to read it. Once the addition is done i am going to be heating with baseboard hot water heat. The boiler will be 3 zones for the just for the new addition and the 4th zone will be added at a later date to accommodate the existing structure of the home. I know at first it will be oversized but when i start the renovation of the existing I will be adding that 4th zone. looking to rid my house of forced hot air. The entire structure will be almost 3000 sqft home all home no garage unfortunately. i am not looking to over size or undersize.
 
  #4  
Old 06-10-13, 04:20 PM
U
Member
Thread Starter
Join Date: Jun 2013
Location: USA
Posts: 6
Received 0 Votes on 0 Posts
I am looking at the heat lose/gain under heating summary:

Structure 45424 Btuh
Ducts 22135 Btuh
Central Vents 0 Btuh
Humidification 0 Btuh
Piping 0 Btuh
Equipment Load 67559 Btuh
 
  #5  
Old 06-10-13, 06:06 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 18,138
Received 55 Votes on 48 Posts
Moved post to its own thread....


The entire structure will be almost 3000 sqft
Probably need around 75k btu boiler. Your 130k btu boiler will be almost twice the size needed. Need to do a heat loss with the free calculator in this link/sticky... ( Sorry it was actually in the boiler section)

I will do some gas calcs tomorrow for you.



http://www.doityourself.com/forum/bo...alculator.html
 
  #6  
Old 06-12-13, 05:53 AM
U
Member
Thread Starter
Join Date: Jun 2013
Location: USA
Posts: 6
Received 0 Votes on 0 Posts
Ok went over all of it and looks like i will be going with an 80k Btu boiler a bit oversized at first but will be adding the 4th zone for the existing home which right now is heated with forced hot air. With the new addition i wont have time until next year to add the 4th zone.
 
  #7  
Old 06-12-13, 08:17 AM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 18,138
Received 55 Votes on 48 Posts
Yes at 80 ft and almost 300k btu you need to come in with 1 1/4"
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: