Bring it up to code while installing new kitchen and replacing tub with shower
#1
Member
Thread Starter
Join Date: Apr 2012
Location: USA
Posts: 82
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Bring it up to code while installing new kitchen and replacing tub with shower
Our house was built in the 50's. We live in eastern Colorado about 8 miles from a small town. I am rewiring the upstairs, installing a kitchen upstairs, and swapping the old tub for a new shower. The old plumbing is copper. I plan on using either PVC or ABS for the new parts. My first question is should I use PVC or ABS? Attached are drawings of before and after for your opinions, suggestions, and corrections. The new kitchen is about 25 feet from the existing vent pipe. Can I use 1-1/2 inch for the kitchen run and dump it into the old tub/new shower pipe or should I use 2 inch and dump it into the vent stack?
#2
Forum Topic Moderator
A few comments:
- The shower drain needs to be 2"
- You want the kitchen drain to go directly into your main, not into the shower drain, nor into the main stack as that will create a wet vent.
- You can use 1.5" for the kitchen drain. No need for 2"
Otherwise looks good to me. I'm sure others may have comments too. Good luck!