gas pipe sizing for small commercial build out

Reply

  #1  
Old 12-03-13, 08:25 AM
J
Member
Thread Starter
Join Date: Dec 2013
Location: United States
Posts: 1
Received 0 Votes on 0 Posts
gas pipe sizing for small commercial build out

I would like to attempt to run a new gas line to a commercial suite that I just leased and need some help determining the size of my gas line.

I have 3 loads at the end of my system. 2 x 80,000 Btu heating units and 1 x 40,000 Btu water heater.

The gas meter is at the far end of the building. I have to run up vertically from the meter to the roof, across the roof, and then down into my unit before I split to the 3 loads. All in all, I am figuring the distance from the meter to my furthest appliance (the water heater) is about 230 feet. 6 elbows would be needed to get to the water heater.

My heating units call for a minimum of 5 inches of water column at the inlet to fire correctly.

The gas company delivers 6 inches of water column to the meter.

Any help would be greatly appreciated.

Thanks!

jds
 
Sponsored Links
  #2  
Old 12-03-13, 09:59 AM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 18,138
Received 55 Votes on 48 Posts
Your looking at 1 1/4" pipe to supply your 200k btu... Thats a lot of black pipe...

Possibly you can read what the meter plate says for us? Possibly you can ask the gas company to increase the pressure so you can run smaller pipe?

If commercial it may be higher pressure already...

Permits are being taken out right?
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: