I am updating a old house and it has a house trap. 4" cast
Is this a nessary trap?, As my main waste line needs some updating and I would like to remove the trap going to 3" sch 40 and connecting one to the other with a Fernco
 
Sponsored Links
  #2  
Old 02-27-01, 07:15 AM
Plumber2000's Avatar
Member
Join Date: May 2000
Location: Eugene, Oregon
Posts: 5,841
Received 0 Votes on 0 Posts
Yes you can do this, as long as you know each fixture in your house has it's own trap.

If the mainline is 4" you need to stay 4" and not reduce it down.
 
  #3  
Old 02-28-01, 04:58 AM
Guest
Visiting Guest
Posts: n/a
My house has only five fixtures in it , a 3" wast line is not large enough through the house? Even if the old cast is 4" running out of the house ?
 
  #4  
Old 02-28-01, 05:50 AM
Plumber2000's Avatar
Member
Join Date: May 2000
Location: Eugene, Oregon
Posts: 5,841
Received 0 Votes on 0 Posts
You can use 3", it's large enough, the thing is, if there is 4" all the way to the toilet/s, between the trap and house, then you have to replace all that 4" to 3", at no point in a line can you decrease a drain line from a larger line, you can increase but not decrease.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: