Propane Piping
Need some help with propane pipe sizing on a new construction.
In Arizona at about 7,000 ft elevation.
Will be using 2 - 100# propage tanks connected to a Camco Automatic Changeover 2-Stage Propane Regulator for Dual Propane Tanks.
Will be using black pipe throughout but not sure on the sizing. Here is a image of what we are planning:

Any thoughts would be greatly appreciated.
In Arizona at about 7,000 ft elevation.
Will be using 2 - 100# propage tanks connected to a Camco Automatic Changeover 2-Stage Propane Regulator for Dual Propane Tanks.
Will be using black pipe throughout but not sure on the sizing. Here is a image of what we are planning:

Any thoughts would be greatly appreciated.
#2
Banned. Rule And/Or Policy Violation
Join Date: Apr 2013
Location: USA
Posts: 4,294
Received 0 Votes
on
0 Posts
Not sure how it works there but any place I've lived you need permits and the gas company or a licensed plumber with a gas license would be designing and sizing this.
And none of them would be counting on 2, 100 LB tanks for what your asking.
More likely an underground at least 275 gal. tank.
And none of them would be counting on 2, 100 LB tanks for what your asking.
More likely an underground at least 275 gal. tank.
#3
Member
Thread Starter
Join Date: Dec 2014
Posts: 12
Received 0 Votes
on
0 Posts
Thanks for your post, but without getting too far off topic, this is permitted and can be done as DIY and will be inspected and the inspector has already approved the use of 2 100# tanks.
I had planned on using 1" as the main trunk line, and reducing to 3/4", but not sure if that is overkill.
Anyone have any thoughts on the sizing? In addition, can the line be too big?
Thanks!
I had planned on using 1" as the main trunk line, and reducing to 3/4", but not sure if that is overkill.
Anyone have any thoughts on the sizing? In addition, can the line be too big?
Thanks!
#4
Cant see your pic close enough...
Whats total btu load of all appliances?
What is the farthest appliance from the refulator? ( I would assume the regulator will be near the house somewhere?
Whats total btu load of all appliances?
What is the farthest appliance from the refulator? ( I would assume the regulator will be near the house somewhere?
#5
Member
Thread Starter
Join Date: Dec 2014
Posts: 12
Received 0 Votes
on
0 Posts
60,000 BTU BBQ
60,000 BTU Furnace
Not sure on the generator. Probably 30,000 BTU
So call it about 150,000 BTU.
The furnace is about 46 Ft. from the Regulator
BBQ is about 24 ft. from the Regulator
and the Generator stub out is about 51 ft. from the Regulator
Thanks!
60,000 BTU Furnace
Not sure on the generator. Probably 30,000 BTU
So call it about 150,000 BTU.
The furnace is about 46 Ft. from the Regulator
BBQ is about 24 ft. from the Regulator
and the Generator stub out is about 51 ft. from the Regulator
Thanks!
#10
The generator is 15-HP
10000 watt gen?
So at 1/2 load thats 7.5 hp to get 5000 watts out of gen... 7.5 x 10000 btu = 75000 btu per hour consumption..
You can run that gen 29 hours on one LP 100# tank..
With that said I beleive you will need to enter the home from the regulator with 1" pipe..
#13
1" from the regulator to the first tee..
1/2" from that tee to the BBQ
1" from that tee to the next tee to furnace and generator.
1/2" form 2nd tee to furnace
3/4" from second tee to generator.
Why not use tract pipe???
You can use their specifier here...
CSST Installation Instructions - Windows, How To Install
After you down load read the instruction on how to use...
http://www.tracpipe.com/customer-con...ev_10-9-07.pdf
I did your calc on paper...( In my head)..
If you download this and try it let me know how it works....
1/2" from that tee to the BBQ
1" from that tee to the next tee to furnace and generator.
1/2" form 2nd tee to furnace
3/4" from second tee to generator.
Why not use tract pipe???
You can use their specifier here...
CSST Installation Instructions - Windows, How To Install
After you down load read the instruction on how to use...
http://www.tracpipe.com/customer-con...ev_10-9-07.pdf
I did your calc on paper...( In my head)..
If you download this and try it let me know how it works....
#14
Member
Join Date: Aug 2012
Posts: 230
Received 0 Votes
on
0 Posts
My 7 KW generator uses 1.47 gal/hr (propane) at full load and 0.82 gal/hr at half load. 23.6 gal in your 100 lb tank. I mounted my (11" wc) regulator at the generator and ran a 10 PSI line from the tank regulator.
#15
and 0.82 gal/hr at half load. 23.6 gal in your 100 lb tank.
I mounted my (11" wc) regulator at the generator and ran a 10 PSI line from the tank regulator.
Just a not I am not a propane guy. Just using my NG experience to calculate...I am not sure of the protacal/codes on where the regulators can be placed... Normally one before the pipe enters the home...
#16
Member
Thread Starter
Join Date: Dec 2014
Posts: 12
Received 0 Votes
on
0 Posts
lawrosa... thank you!!
I have updated my image with your recommendations. Is this what you were thinking?

I will also check out the tracpipe info. Thanks for providing it.
DMCman.... thanks for calcs. I was unsure on the amount that the generator might use and this helps!!
Really appreciate the insight guys!!! Thanks!!!
I have updated my image with your recommendations. Is this what you were thinking?

I will also check out the tracpipe info. Thanks for providing it.
DMCman.... thanks for calcs. I was unsure on the amount that the generator might use and this helps!!
Really appreciate the insight guys!!! Thanks!!!
#18
Member
Thread Starter
Join Date: Dec 2014
Posts: 12
Received 0 Votes
on
0 Posts
Inlets are 1/4" SAE inverted flare and outlet is 3/8" NPT female pipe thread.
I suspect I may need to get a large regulator? If you think so, you don't happen to have a recommendation do you?
I suspect I may need to get a large regulator? If you think so, you don't happen to have a recommendation do you?
#19
Best off to call LP company and ask... The camco is for campers and short runs IMO. I think its a 2 stage that gets installed for volumes. Dont know what they have for auto switching....
#22
Mike, out of curiosity, is the yellow piping you are suggesting the plastic only? I have never run across it, literally, until the other day. I had 811 do a locate for me, and all the utilities were on the front side of the house. EXCEPT for a run of the yellow plastic to the back of the house for a grill installation (.65 diameter). No tracer wires so no locate. My electric trench went right through it. Luckily the customer was unaware it existed and wanted it abandoned anyway, but it was scary hearing the gas leaking. I guess the caution here is install tracer wire as you install the plastic.
#23
Member
Thread Starter
Join Date: Dec 2014
Posts: 12
Received 0 Votes
on
0 Posts
The propane company recommended this regulator:
Marshall Excelsior - MEGR-253
We also talked about the lines and oversized lines will not create an issue. Better to have too big than not enough.
Yeah, if you are doing underground definitely run a tracer wire. They inspect for them here on water, sewer, and propane before you can back fill.
Great forum here and thanks for everyone's help and insight!!!!
Marshall Excelsior - MEGR-253
We also talked about the lines and oversized lines will not create an issue. Better to have too big than not enough.
Yeah, if you are doing underground definitely run a tracer wire. They inspect for them here on water, sewer, and propane before you can back fill.
Great forum here and thanks for everyone's help and insight!!!!
#24
The propane company recommended this regulator:
Marshall Excelsior - MEGR-253
Marshall Excelsior - MEGR-253
We also talked about the lines and oversized lines will not create an issue. Better to have too big than not enough.
The line size I suggested?
Mike, out of curiosity, is the yellow piping you are suggesting the plastic only?
The line you had under ground was gas poly... Someone failed to install tracer wire...
#25
I may have used the wrong chart... I need to look when I get time....
Those sizes I gave you may be wrong...
http://www.regoproducts.com/pdfs/L-5...ans_Manual.pdf
Those sizes I gave you may be wrong...
http://www.regoproducts.com/pdfs/L-5...ans_Manual.pdf