Big time hammering/shaking of pipes after PEX add on install.
#1
Member
Thread Starter
Big time hammering/shaking of pipes after PEX add on install.
I have no pics, but can get some of what I am talking about if needed. I am thinking a faulty valve, the reason follows below. But looking for other opinions before I tackle this in the morning.
This is on main 1/2" iron waterline. There was a T on this, with a spigot used for outdoor watering from inside.
I removed that spigot and put a T with a 1/2" gate(type) valve before it. Off that new "T" I ran the same spigot as well as an added 1/2" male adapter for PEX line. I ran that PEX line up and over to an outdoor sillcock valve.
When I turn on the valve before the T to allow water to go to the spigot and PEX run, I get massive shuddering in the main line. It does not go away. As I open up that gate valve, I hear the hissing of water starting to go through like I have hear 1,000 times. But that stops, as does any trickle of water. It takes a couple more turns with no water flow and that is when the hammering/shuddering starts. I tried it with the PEX line end valve open with the same result(was figuring trapped air)
First time I have experienced anything like this in this house. It seems to me the problem lies in the new gate valve....as it seems to let water start going through then stops. I am going there tomorrow to replace that valve, unless it may be something else?
This is on main 1/2" iron waterline. There was a T on this, with a spigot used for outdoor watering from inside.
I removed that spigot and put a T with a 1/2" gate(type) valve before it. Off that new "T" I ran the same spigot as well as an added 1/2" male adapter for PEX line. I ran that PEX line up and over to an outdoor sillcock valve.
When I turn on the valve before the T to allow water to go to the spigot and PEX run, I get massive shuddering in the main line. It does not go away. As I open up that gate valve, I hear the hissing of water starting to go through like I have hear 1,000 times. But that stops, as does any trickle of water. It takes a couple more turns with no water flow and that is when the hammering/shuddering starts. I tried it with the PEX line end valve open with the same result(was figuring trapped air)
First time I have experienced anything like this in this house. It seems to me the problem lies in the new gate valve....as it seems to let water start going through then stops. I am going there tomorrow to replace that valve, unless it may be something else?
#2
Member
Gate valves can do all sorts of weird things when not fully open or fully closed. It's also possible yours is just defective. I suggest you replace it with a ball valve; they are superior to gate valves in many ways.
#3
Member
Join Date: Jun 2016
Location: United States
Posts: 1
Upvotes: 0
Received 0 Upvotes
on
0 Posts
This is James77. For whatever reason, I could not keep positng under that name after that thread. Emails to admins were not responded to. There is no reason why I would be banned, maybe some fluke?
Anyways....I replaced the valve with a ball valve and all is well. So it was a bad valve.
Thank you for the response
Anyways....I replaced the valve with a ball valve and all is well. So it was a bad valve.
Thank you for the response

#4
You were not banned. You probably joined the board from a social media source rather than signing up directly at DIY.