AAV not venting


  #1  
Old 11-04-17, 03:10 PM
Z
Forum Topic Moderator
Thread Starter
Join Date: Sep 2005
Location: USA
Posts: 5,874
Received 372 Upvotes on 332 Posts
AAV not venting

I upgraded an old laundry sink recently. The 1.5" drain goes into the basement slab (to a recently jetted main sewer line). The above-ground was changed to new PVC, sanitary tee to the laundry sink p-trap, then up to about 50" or so where there's an AAV. Looks pretty and plumbed nicely.

Started off with an ABS 'cheater' vent.


The drain now drains slowly. It does drain, but very slowly. As soon as I removed the vent, draining went back to normal fast draining.

I figured it was the cheap vent I chose, so upgraded to a Studor Redi-Vent


Same problem. It doesn't drain well with the AAV. Remove the vent - and it's all good.

What's next? I can't figure out why the AAV isn't working as it should. Thanks in advance!
-Mike
 
  #2  
Old 11-20-17, 10:29 AM
Z
Forum Topic Moderator
Thread Starter
Join Date: Sep 2005
Location: USA
Posts: 5,874
Received 372 Upvotes on 332 Posts
I'm still having this issue, and short of completely removing the AAV, I'm stumped. Open pipe, sink drains perfectly. Screw in the AAV, sink drains really slowly. Any thoughts or suggestions?

Name:  IMG_3817.jpg
Views: 2099
Size:  88.9 KB
 
  #3  
Old 11-20-17, 11:17 AM
Handyone's Avatar
Member
Join Date: Aug 2000
Location: U.S.
Posts: 4,807
Upvotes: 0
Received 0 Upvotes on 0 Posts
I'm not positive it will fix the problem, I think so. Instructions for an AAV state the mark/line should be 6" above the top of the trap line.
I would say the vent is too high.
 
Attached Images  
  #4  
Old 11-20-17, 11:41 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,494
Received 3,484 Upvotes on 3,128 Posts
"Must be located at least 6" above the trap arm."
They give you an "at least" but not a maximum.
 
  #5  
Old 11-20-17, 11:49 AM
Handyone's Avatar
Member
Join Date: Aug 2000
Location: U.S.
Posts: 4,807
Upvotes: 0
Received 0 Upvotes on 0 Posts
The fact that the pipe drains when the AAV is removed tells you the AAV is not working.
I have the exact same set up in my garage and the vent works fine at 6".
 
  #6  
Old 11-20-17, 11:53 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,494
Received 3,484 Upvotes on 3,128 Posts
I'm not arguing. They should specify that an extended length will hinder the performance. Something like 6" minimum and not over 15".
 
  #7  
Old 11-20-17, 11:57 AM
Handyone's Avatar
Member
Join Date: Aug 2000
Location: U.S.
Posts: 4,807
Upvotes: 0
Received 0 Upvotes on 0 Posts
Very true.........................................
 
  #8  
Old 11-20-17, 02:58 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 15,984
Received 79 Upvotes on 71 Posts
The vent is not for draining purposes. The vent is so the trap does not get siphoned when other fixtures are used.

Think about it. Without a vent the fixtures will drain as the drain itself works as a so called bent.

I mean look at a toilet vent... Take the toilet vent away and the toilet will operate the same without it. The vent on the toilet is so other fixtures dont siphon the water out to release sewer gas..

I can probably bet if you drop that trap and snake that line to the main your issue will go away.....

That could be a shallow pitched line running under the slap to the main..

Plus laundry line means lint build up. Especially where the y meets the main under slab..

Just my opinion from my experience...

It is usually a misconception to conclude that a bad, or lack of a, vent causes slow drainage. ALL fixtures are vented automatically....air can enter behind the water right through the sink, tub, etc drain. The problem with that is that is takes the trap water with it!
A blocked vent can cause some gurgling in OTHER fixtures, etc. but in general the stuff will drain.
terrylove.com
 
  #9  
Old 11-21-17, 09:58 AM
Z
Forum Topic Moderator
Thread Starter
Join Date: Sep 2005
Location: USA
Posts: 5,874
Received 372 Upvotes on 332 Posts
I can probably bet if you drop that trap and snake that line to the main your issue will go away.....
I will try that... BUT - the part that is driving me crazy is that when the vent is screwed in, I can hear the water literally dripping down the vertical part of the PVC, like a just barely running tap.

Unscrew the vent, and woosh - drains as fast as you'd expect.


Thinking about it more... maybe you're right Mike. A partial clog is just blocking it enough to fill the pipe and start a vacuum, thus causing the slow drain. But it's not enough of a clog to actually slow down the draining of the water on its own.

Ok, fine - you've convinced me to snake the branch. I'll let you know how it goes.

Thanks!
 
 