Pipe size for LP to fireplace

I recently installed an LP fireplace 45,000 btu and had a plumber run the black pipe to a place where a tank would be dropped. He ran 32 total feet in 1/2 inch. The gas company recommended extending the run to a different location. This would require 38 additional feet. So the total distance would be 70’. Is it ok to continue with 1/2”?
Cheers!
 
  #2  
Old 04-04-18, 03:31 PM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 26,284
Received 1,840 Upvotes on 1,647 Posts
At 70 feet length 1/2" pipe has the capacity for about 75'000 btu so you should be good with a healthy margin.
 
 