Long washer drain pipe?

Can I install a drain pipe to connect a moved washer to an older basement washer drain 30 feet away? If the slope is 1/4" per foot then that's 7.5", so that doesn't sound bad.
 
Sponsored Links
  #2  
Old 06-08-18, 05:43 PM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 23,432
Received 590 Votes on 544 Posts
You will also need a vent.
 
  #3  
Old 06-08-18, 08:41 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 58,501
Received 1,029 Votes on 955 Posts
You'll also need, I believe, at least a 2" line to handle the amount of water without backing up.
 
  #4  
Old 06-10-18, 03:21 AM
maarkr's Avatar
Member
Thread Starter
Join Date: Mar 2014
Location: United States
Posts: 363
Received 7 Votes on 5 Posts
so if it's going to a previously installed and vented drain, I shouldn't need another vent near the washer?
 
  #5  
Old 06-10-18, 05:33 AM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 23,432
Received 590 Votes on 544 Posts
Re-read post #2. You need a vent.
 
  #6  
Old 06-10-18, 06:30 PM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 5,258
Received 102 Votes on 95 Posts
For a 2" drain, the max distance from the trap to the vent is 60" (5').
For a 1.5" drain, the max distance is 42" (3.5')

Your locale may allow the use of AAVs (Studor vents) so it may provide a good way to vent.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: