See anything wrong with this laundry standpipe
Old 11-30-19, 11:43 PM
I had a plumber put in a standpipe for my washer, the left vertical pvc pipe has a studer valve on top.
Curious if anyone else see something wrong with how this is configured.
thanks
Old 12-01-19, 03:47 AM
Received 60 Votes on 56 Posts
Is this a trick question?
Looks OK to me.
The real question is "Does it work OK?"
Old 12-01-19, 05:41 AM
Norm201's Avatar
Received 109 Votes on 100 Posts
Looks funny, but nothing is wrong. It's trapped and then goes into a vertical drain. If there was a wall right after the trap as it enters the wye, you would not question it. I think because it twisted for alignment purposes makes it look odd.
Old 12-01-19, 07:39 AM
Received 305 Votes on 279 Posts
Is the air admittance valve (AAV) out in the open or buried in the wall cavity? It cannot be concealed because they do fail and need to be replaced occasionally. If it's inside the wall cavity there should be an access panel so you can service it in the future.
Old 12-01-19, 10:42 AM
CasualJoe's Avatar
Received 40 Votes on 32 Posts
I would have used a San Tee instead of a Wye, but I believe the Wye is acceptable. The AAV may or may not be allowed, check with your AHJ for details.
Old 12-01-19, 04:41 PM
CasualJoe: I agree.
I believe the wye fitting restricts vent air, and I don't think he had the min of 4inch run.
thanks
Old 12-03-19, 06:25 PM
Received 36 Votes on 35 Posts
I assumed you were concerned about the 'twisting' of the trap. No issue there. It looks odd, but totally normal.
I've never heard an issue with a combo wye used in that position... but I too would have used a sanitary tee by default. Maybe I'm just not familiar enough with the DWV patterns.
Old 12-03-19, 07:19 PM
lawrosa's Avatar
Super Moderator
Received 37 Votes on 32 Posts
Thats considered a long sweep and change of direction. Its OK. with a san tee you need some inches of pipe to the san tee. with a st fitting in a wye it becomes a long sweep.
Were are you that you follow the UPC?
IPC says.
TABLE 706.3 FITTINGS FOR CHANGE IN DIRECTION
Zorfdt voted this post useful.
Old 12-08-19, 12:33 AM
Received 3 Votes on 2 Posts
That's not really a change of direction, it's where a drain, vent and trap arm to a p-trap meet. It should be a tee.
HTML code is On