Reuse gas threaded steel pipe and installation?


  #1  
Old 09-22-20, 02:14 PM
9
Member
Thread Starter
Join Date: Nov 2006
Location: USA
Posts: 140
Upvotes: 0
Received 0 Upvotes on 0 Posts
Reuse gas threaded steel pipe and installation?

Hi,

I have a ventless natural gas heater that needs to be replaced. It is located in the garage and is I believe connected with black steel threaded pipe with a Union connection near which allows me to add a new ventless natural gas heater easier. I have some question:

The threaded fittings have pipe dope on it. Can I reuse the black steel pipe threaded fittings if I unthread it? Or is the union connection the only fitting I can reuse? I assume I can reuse the union fitting viewed below:








Finally this is the pipe dope that I plan on using with black steel threaded pipe for the natural gas:



 
  #2  
Old 09-22-20, 04:46 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
Black iron pipe lasts almost forever. Perfectly acceptable to reuse it.
I never throw any threaded pipes, nipples or fittings away.

Use a wire brush to clean all the old dope out of the threads and apply new.
That dope is fine for gas piping.
 
Drangd voted this post useful.
  #3  
Old 09-22-20, 06:38 PM
9
Member
Thread Starter
Join Date: Nov 2006
Location: USA
Posts: 140
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks PJmax, read stuff online that seemed to indicate that it wasn't acceptable which didn't make much sense to me.
 
 