Reuse gas threaded steel pipe and installation?
#1
Member
Thread Starter
Join Date: Nov 2006
Location: USA
Posts: 140
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Reuse gas threaded steel pipe and installation?
Hi,
I have a ventless natural gas heater that needs to be replaced. It is located in the garage and is I believe connected with black steel threaded pipe with a Union connection near which allows me to add a new ventless natural gas heater easier. I have some question:
The threaded fittings have pipe dope on it. Can I reuse the black steel pipe threaded fittings if I unthread it? Or is the union connection the only fitting I can reuse? I assume I can reuse the union fitting viewed below:

Finally this is the pipe dope that I plan on using with black steel threaded pipe for the natural gas:

I have a ventless natural gas heater that needs to be replaced. It is located in the garage and is I believe connected with black steel threaded pipe with a Union connection near which allows me to add a new ventless natural gas heater easier. I have some question:
The threaded fittings have pipe dope on it. Can I reuse the black steel pipe threaded fittings if I unthread it? Or is the union connection the only fitting I can reuse? I assume I can reuse the union fitting viewed below:

Finally this is the pipe dope that I plan on using with black steel threaded pipe for the natural gas:

#2
Black iron pipe lasts almost forever. Perfectly acceptable to reuse it.
I never throw any threaded pipes, nipples or fittings away.
Use a wire brush to clean all the old dope out of the threads and apply new.
That dope is fine for gas piping.
I never throw any threaded pipes, nipples or fittings away.
Use a wire brush to clean all the old dope out of the threads and apply new.
That dope is fine for gas piping.