Expansion Tank


  #1  
Old 08-28-21, 01:23 PM
W
Member
Thread Starter
Join Date: Feb 2006
Location: USA
Posts: 6,345
Received 60 Upvotes on 52 Posts
Expansion Tank

What size expansion tank do I need for a 50 gallon electric water heater?
 

Top Answer

 
09-01-21, 03:58 PM
AllanJ
AllanJ is offline
Member
Join Date: Mar 2010
Location: USA
Posts: 4,347
Upvotes: 0
Received 250 Upvotes on 230 Posts
Preset the expansion tank to approximately the static pressure, 70 PSI. Ever few minutes during the presetting process (using an air pump) open a faucet upstairs so the expansion tank bottoms out at that approx. 70 PSI.

Seventy PSI in from the water main is a little on the high side for home pressure. For this I suggest a 3 or 4 gallon expansion tank.


I estimate that the worst case expansion is one gallon to heat all 50 gallons water up from an incoming 50 degrees F to 120 degrees. When that increase squeezes into the 2 gallon expansion tank the air cushion will have half of the space it occupied before, which means its pressure (and the pressure everywhere else in the system) will double making 140 PSI.

If you preset the expansion tank lower, say, to 50 PSI, the system pressure will still go to 70 PSI when all the faucets are turned off. With the lower preset pressure, water will go into the expansion tank even before the water heater raises its temperature. This leaves less space in the expansion tank for when the water starts expanding from being heated.
 
  #2  
Old 08-29-21, 12:43 PM
badeyeben's Avatar
Member
Join Date: Dec 2006
Location: Southern ILLINOIS
Posts: 1,144
Received 54 Upvotes on 48 Posts
I found this when I searched. You need a thermal expansion solution that is adequately sized for your plumbing system. One 50-gallon water heater, for instance, can be served by a 2-gallon expansion tank. If you have more than one heater on the same or connected system you can either have an expansion tank for each heater or a single, larger expansion tank.
 
  #3  
Old 08-30-21, 06:11 AM
W
Member
Thread Starter
Join Date: Feb 2006
Location: USA
Posts: 6,345
Received 60 Upvotes on 52 Posts
Thanks, Ben. What air pressure should I set?
When using water the line pressure is 50 psi. When not using water, the line pressure is 70 psi.
 
  #4  
Old 09-01-21, 03:58 PM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,347
Upvotes: 0
Received 250 Upvotes on 230 Posts
Preset the expansion tank to approximately the static pressure, 70 PSI. Ever few minutes during the presetting process (using an air pump) open a faucet upstairs so the expansion tank bottoms out at that approx. 70 PSI.

Seventy PSI in from the water main is a little on the high side for home pressure. For this I suggest a 3 or 4 gallon expansion tank.


I estimate that the worst case expansion is one gallon to heat all 50 gallons water up from an incoming 50 degrees F to 120 degrees. When that increase squeezes into the 2 gallon expansion tank the air cushion will have half of the space it occupied before, which means its pressure (and the pressure everywhere else in the system) will double making 140 PSI.

If you preset the expansion tank lower, say, to 50 PSI, the system pressure will still go to 70 PSI when all the faucets are turned off. With the lower preset pressure, water will go into the expansion tank even before the water heater raises its temperature. This leaves less space in the expansion tank for when the water starts expanding from being heated.
 
Wirepuller38, Zorfdt voted this post useful.
  #5  
Old 09-02-21, 06:34 AM
W
Member
Thread Starter
Join Date: Feb 2006
Location: USA
Posts: 6,345
Received 60 Upvotes on 52 Posts
Thank you, AllanJ.
 
 