I have recently acquired a “triple fuel” generator with the desire to run it on natural gas. That is all the previous owner used. He generously provided a new spare set of “quick connect” fittings for the provided gas line that I intend to use for ease of connection to supply. I have a utility bathroom water heater closet on an exterior wall that has a natural gas supply. I intend to tap in there and run thru the wall to an exterior valve and quick connect station. I’m thinking of installing some type of weather right box to house this in. Looking for any suggestions here or examples of this setup that someone else has installed.

Regards

TF
 
  #2  
Old 03-17-22, 12:11 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,102
Received 3,424 Upvotes on 3,070 Posts
Running a generator on natural gas is a great idea.
However... the generator requires a good flow of natural gas and the line that feeds the water heater may not be large enough to handle both.

Gas CFM can be computed based on supply line size and length.
You also need to know the CFM required by the genny.
You can post the make and model of the genny and I can tell you what that uses.
 
Zorfdt voted this post useful.
  #3  
Old 03-18-22, 05:08 AM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 25,975
Received 1,776 Upvotes on 1,588 Posts
Generators consume a lot of gas. For example, my generator consumes 327'000 btu of natural gas at full load. That is a HUGE amount and more then most home gas piping can supply, but it's also a biggish generator. You really need to look at the specs for your generator's fuel consumption. Then you can do the math to see if your piping can carry enough gas. You need to check your pipe size from the meter all the way to the generator.

You also should check the capacity of your meter. Smaller ones are only capable of delivering 175'000 btu/hour but bigger ones are also common but they are usually sized for load so you might not have a lot of reserve capacity left and need a larger meter. The meter should have it's capacity listed on it's data plate. If it's in cubic feet per hour multiply by 1'000 to get it's approx capacity in btu.

 
Zorfdt voted this post useful.
  #4  
Old 03-20-22, 06:13 AM
T
Member
Thread Starter
Join Date: Oct 2010
Location: USA
Posts: 257
Received 1 Upvote on 1 Post
The generator is a Firman T07571. I’m also attaching a pic of my gas meter plate. The discharge elbow above the Union on my meter has a 1/4” tap, I can likely swap that for a tee and provide a connection point for the 35’ supply hose directly from there.

TF

 
  #5  
Old 03-20-22, 10:59 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,102
Received 3,424 Upvotes on 3,070 Posts
Your gas meter is 195 cfh. So that is ok.
Firman specs:
7-11 inches water column (0.25-0.40 psi)
101 cfh of natural gas at max load.


Based on the genny specs.... your 35' hose ? would need to be 3/4".

 
  #6  
Old 03-21-22, 01:54 PM
T
Member
Thread Starter
Join Date: Oct 2010
Location: USA
Posts: 257
Received 1 Upvote on 1 Post
Wow. The hose that came with it is 3/8”. I’m gonna try and find a 10’ 1/2” hose. Thanks for the input!

TF
 
  #7  
Old 03-21-22, 01:55 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,102
Received 3,424 Upvotes on 3,070 Posts
Normally you'd run 3/4" or 1" pipe and then use a short interconnect hose.
 
  #8  
Old 03-24-22, 07:12 PM
T
Member
Thread Starter
Join Date: Oct 2010
Location: USA
Posts: 257
Received 1 Upvote on 1 Post
OK. I’ve located a 10’ natural gas hose 1/2” inside diameter with a quick connect fitting. My plan is to replace the elbow at the gas meter discharge with a 1”x1” with a 1/2” tap as opposed to 1/4” as currently situated. I’ll add a street elbow, a nipple and a gas cutoff valve and then the quick connect female for connecting my hose. I noted a reference to NFPA 54 / ANSI Z223.1. Will my plan be suitable with these regs?

TF



 
  #9  
Old 03-24-22, 08:31 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,102
Received 3,424 Upvotes on 3,070 Posts
As far as I know... yes. I'm not a licensed plumber so I don't deal with these jobs all the time.
I'm just supplying info based on my knowledge and past install history.
 
  #10  
Old 04-01-22, 08:48 PM
T
Member
Thread Starter
Join Date: Oct 2010
Location: USA
Posts: 257
Received 1 Upvote on 1 Post
Well I bought all of the fittings to add a 1” tee at that discharge 90 elbow with a bushing to 1/2” and a gas valve to the quick connect. My gas company contact then advised that 1/4” tap has to stay as that is where they tie in to calibrate the regulator so I’ll need to add some more fittings. I’ll post a pic when it’s done.
 
  #11  
Old 04-02-22, 06:24 AM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 15,984
Received 79 Upvotes on 71 Posts
Take a pic of the gas company's regulator. Often here in SC we get a meter upgrade to 2psi. Then we regulate. you can better control gas flow that way.

Yes that tap has to stay.

I am surprised they are letting you as a homeowner break into the meter..

Not allowed in most states AFAIK
 
 