Washer dishcharge into vent question

Hello

I am putting washer and dryer on main floor.

When opening the wall found pipe in picture.

There isn't anything directly above this on next floor but a wall.

I suspect it is the vent for the bathroom on the other side of the pipe wall in picture.

The bathroom sink etc are not against the wall.

I was going to take the discharge down to the basement but since this pipe is there is it acceptable to cut into this vent and discharge there?


 
  #2  
Old 02-13-23, 07:51 PM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 5,834
Received 367 Upvotes on 327 Posts
As far as I'm aware, no, it's not permitted. Wet vents can be used within the bathroom group, but since the laundry is outside the bathroom, I don't believe UPC/IPC allows it.

I would recommend a 2" drain down to the basement and tie in down there. Then at at least 42" high, tie into the vent to vent your new washer drain.
 
  #3  
Old 02-14-23, 04:57 AM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 25,979
Received 1,776 Upvotes on 1,588 Posts
That looks like 1 1/2" pipe in the wall. You can't use it for several reasons. The biggie is that you cannot use that vent as a drain. And, a washer requires a minimum of 2" drain piping in addition to needing a trap and must have a vertical pipe 18-42" above the water level of the trap.

Go ahead and remove the strip of sheetrock along the bottom plate. It will have to come off anyhow when you repair the sheetrock.

I would take this opportunity to run a dedicated 20 amp circuit for the washer since you have the wall opened. It's a code requirement for new construction and since you've opened the wall to run plumbing you've technically lost "grandfathering". Your inspectors may let it slide but having the machine on it's own circuit is a good idea anyhow. You don't want to be tripping the breaker when you do laundry.
 
  #4  
Old 02-14-23, 05:17 PM
J
Member
Thread Starter
Join Date: Dec 2019
Location: Canada
Posts: 48
Received 0 Upvotes on 0 Posts
I have done that for the dedicated 20amp cct. I used the old plug lighting cct. to put a plug above where the counter-top will be.

 
  #5  
Old 02-15-23, 07:33 PM
J
Member
Thread Starter
Join Date: Dec 2019
Location: Canada
Posts: 48
Received 0 Upvotes on 0 Posts
2in washer discharge and pex question

1

I will be putting the 2in discharge pipe along the outside of the drywall. I don't see anyway to get it into the wall at this point. The 1.5in pipe in the picture is a vent, how do I use this for the 2in discharge pipe vent? I know I'm asking a simple question but I'm not seeing it.



2

Also the pex I have installed how do I relax the coil in it. Thought of using a heat gun on low.


 
  #6  
Old 02-16-23, 04:55 AM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 25,979
Received 1,776 Upvotes on 1,588 Posts
1. You may NOT. You must have a 2" or larger drain line all the way until it meets the main drain stack for the home.

You might be able to use the 1 1/2" vent pipe as a vent for your washer drain. First you need to find out what (how many) fixtures that vent is already venting. There are charts online that cover all this but a 1 1/2" vent can accommodate up to 8 "units" of venting. A clothes washer counts as three units. So, you need to verify that there are 5 or less units worth of fixtures connected to that vent line.

2. The best way is to uncoil it outside on a sunny day. It is best done before installation because you'll likely have to over bend in the opposite direction to get it to end up where you want.

Grab a hair dryer and you can probably get your installed pipe straightened enough that it won't rub on the sheetrock. Heat the inside of the curve you want to straighten. Then when the pipe is warm over bend it in the opposite direction by about how far it was bent the wrong way. Take the heat away and hold the pipe in the over bent position until it mostly cools. You can rub a wet rag over the pipe to cool it quickly.
 
  #7  
Old 02-16-23, 05:28 AM
XSleeper's Avatar
Group Moderator
Join Date: Dec 2004
Posts: 26,235
Received 1,721 Upvotes on 1,545 Posts
If you are concerned about the kink at the pex elbows below your washer box, you can put a 2x4 horizontally behind them and fasten them with anchors. (Twin Talon or similar)

And I have no idea why you drew your 2" hole where you did... your 2" drain line should be going straight down to the basement within the stud bay directly below the washer box. (And if you can't do that for some reason, you should have put the washer on the right and the dryer on the left.) Assuming the washer IS going where your washer box is located, I'd plumb it like this...

Washer standpipe is 2" pipe no more than 30" tall, (as measured from your washer box) with a trap going to the left. Then you have minimum 4" of horizontal pipe left of the trap weir (called the trap arm) that dumps into a sanitary tee. Bottom of tee continues straight down to the basement. The top part of that tee would usually go straight up into the attic where it would then connect to the other vent line with an elbow, horizontal pipe pitched up 1/4" per ft to a sanitary tee. (As Pilot Dane mentioned, you can vent to your 1 1/2" provided your total DFU on that vent line does not exceed 8 units) But instead of going into the attic, you could tie it back in to the other vent a minimum of 6" above the flood line of the washer box, provided you cut out more drywall above it and drill a hole through the 1 stud to the right of the washer box in order to tie your 2" pipe back into the 1 1/2" vent. And you would reduce the 2" vent line to 1 1/2" before you get to the hole in your stud.
 
Pilot Dane voted this post useful.
  #8  
Old 02-16-23, 09:42 AM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 5,834
Received 367 Upvotes on 327 Posts
Can you move the 2 drain over a stud bay to the left?

2" pipe down to the basement into either a 90 degree long bend and tie into the main drain down there. Or use a combo wye and use the straight opening to add a plug to have somewhere to snake if needed.

Once it goes through the bottom plate, go up about 6-8", then add a sanitary tee. The side opening goes to a trap and up to the vertical standpipe, 18"-30", but higher than the top of the washer.

From the san tee, go up at least 42". Then 90 over through the stud and tie into the bathroom vent via an upside down sanitary tee.

I'm sure I can find a pic or drawing if the description doesn't make sense.
 
  #9  
Old 02-16-23, 06:39 PM
J
Member
Thread Starter
Join Date: Dec 2019
Location: Canada
Posts: 48
Received 0 Upvotes on 0 Posts
Pilot Dane, there are 3 unit using this vent so all should be good. Been using a heat gun for taking the bend out of the pex bit at a time.

 
  #10  
Old 02-16-23, 07:11 PM
J
Member
Thread Starter
Join Date: Dec 2019
Location: Canada
Posts: 48
Received 0 Upvotes on 0 Posts
Zorfdt
Can you move the 2 drain over a stud bay to the left? Not going to work like that, if I did that then the pipe would come out in the ceiling, where I am placing it, it will come out in a cupboard.
See picture if I am understanding you.


 
  #11  
Old 02-16-23, 07:12 PM
XSleeper's Avatar
Group Moderator
Join Date: Dec 2004
Posts: 26,235
Received 1,721 Upvotes on 1,545 Posts
Got to love how the like button puts our replies out of order. My post #8 appears as post #2 now.
 
  #12  
Old 02-20-23, 05:44 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,787
Received 173 Upvotes on 156 Posts
My post #8 appears as post #2 now.
​​​​​​​How did that happen?
 
  #13  
Old 02-20-23, 05:49 PM
XSleeper's Avatar
Group Moderator
Join Date: Dec 2004
Posts: 26,235
Received 1,721 Upvotes on 1,545 Posts
How did that happen
​​​​​​​When someone likes a post, it jumps out of order. They are working on getting it fixed.
 
  #14  
Old 02-21-23, 11:12 AM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 5,834
Received 367 Upvotes on 327 Posts
Yes, your drawing looks good.

Personally, I'd try to keep the horizontal 2" pipe and trap in the wall and come up to the right of the vent pipe with a pair of 45's. But what you have drawn is correct.

Unrelated: check the 14ga cable on the right most of the pic. It's stapled within 1.25" of the face of the stud and is likely to get hit by an errant drywall screw.
 
 