teledyne laars series 2 esg 400 wont fire

teledyne laars series 2 esg 400 wont fire


  #1  
Old 05-01-08, 12:50 PM
gjrfixit's Avatar
New Member
Thread Starter
Join Date: Apr 2008
Location: northeast new jersey
Posts: 13
Received 0 Votes on 0 Posts
teledyne laars series 2 esg 400 wont fire

i filally got pilot to light. puts out 350mv then i by passed redundant,hilimit,and thermostst but still wont fire. help me. thanks
 
  #2  
Old 05-01-08, 07:05 PM
todrut's Avatar
Member
Join Date: Jun 2007
Location: USA
Posts: 1,212
Received 0 Votes on 0 Posts
needs about 500mv to fire, either pilot light needs cleaning or new pilot generator possibly needed.
 
  #3  
Old 05-06-08, 07:33 PM
gjrfixit's Avatar
New Member
Thread Starter
Join Date: Apr 2008
Location: northeast new jersey
Posts: 13
Received 0 Votes on 0 Posts
thanks fixed it

thanks for the info i was told to replace the pilot generator only if it was 250mv or lower. replaced it and works great.
 
  #4  
Old 05-06-08, 08:10 PM
P
Member
Join Date: May 2008
Posts: 1
Received 0 Votes on 0 Posts
Smile

My laars lite 2 had a similar problem. After reading you all I could not tell what was wrong. So this morning I decided to try again at getting my heater to work. The first thing I did was to bypass the on/off switch and guess what the burner came on. My problem was the on/off switch, one terminal was loose and did not make contact so the unit was never on.
Best of luck to you.
 
  #5  
Old 05-07-08, 06:44 AM
todrut's Avatar
Member
Join Date: Jun 2007
Location: USA
Posts: 1,212
Received 0 Votes on 0 Posts
Great news, congratulations...
 
 