Hayward H250 heater?

I am trying to get my heater going and the pilot light will not stay lit. I go through the procedure and it lights correctly but, after holding it down for at least a minute, as soon as I release the control it goes out. Does anyone have any suggestions?
 
  #2  
Old 05-16-08, 05:05 PM
todrut's Avatar
Member
Join Date: Jun 2007
Location: USA
Posts: 1,068
Upvotes: 0
Received 0 Upvotes on 0 Posts
Could be your pilot is not strong enough to create the millivolts needed or the pilot generator might be bad. It is common for spiders to spin web in pilots over winter and cause a lacking flame. Try cleaning the pilot.
 
  #3  
Old 05-16-08, 05:33 PM
N
Member
Thread Starter
Join Date: May 2008
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Well I got the pilot working now the heater will not come on. I can't win.
 
  #4  
Old 05-16-08, 05:40 PM
todrut's Avatar
Member
Join Date: Jun 2007
Location: USA
Posts: 1,068
Upvotes: 0
Received 0 Upvotes on 0 Posts
Give me more info, we'll figure it out. How did you get pilot lit? Is pilot strong flame? Did you test millivolts? Is filter clean? Good circulation?
 
  #5  
Old 05-16-08, 06:36 PM
N
Member
Thread Starter
Join Date: May 2008
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
I just kept trying and it finally stayed lit. I haven’t checked any voltage what do I check? Everything is as clean as can be expected, it’s 7 years old, but I don’t know of any filter on it. I don’t know about circulation as there isn’t anything flowing except the gas for the pilot light and it is burning good.
 
  #6  
Old 05-16-08, 07:12 PM
todrut's Avatar
Member
Join Date: Jun 2007
Location: USA
Posts: 1,068
Upvotes: 0
Received 0 Upvotes on 0 Posts
There still could be a web inside the pilot, take a small wire, bend a very small hook on end and run in and out of pilot holes. Circulation fefers to pool water running through heater. If you have voltmeter, check millivolts being produced on pilot generator.
 
  #7  
Old 05-17-08, 02:08 PM
N
Member
Thread Starter
Join Date: May 2008
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
The water is circulating just fine. I have a volt meter but I don't know where the reading should be taken for the pilot voltage. There is a line coming up from the pilot to the main control valve should I check this line?
 
  #8  
Old 05-17-08, 08:17 PM
todrut's Avatar
Member
Join Date: Jun 2007
Location: USA
Posts: 1,068
Upvotes: 0
Received 0 Upvotes on 0 Posts
check millivolts on the two wires coming from the pilot.
 
  #9  
Old 05-18-08, 08:42 AM
N
Member
Thread Starter
Join Date: May 2008
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
The way this thing is built it’s impossible to get to the pilot without taking the whole heater apart. The wire that comes up from the pilot area to the main control valve shows .5 volts with my meter set on 2 volts DC.
 
  #10  
Old 05-18-08, 05:13 PM
todrut's Avatar
Member
Join Date: Jun 2007
Location: USA
Posts: 1,068
Upvotes: 0
Received 0 Upvotes on 0 Posts
If you take a small piece of wire or a wire with aligator clips on ends and trip heater safety loop at valve and it lights I would definately clean pilot. If not let me know.
 
  #11  
Old 05-26-08, 10:03 PM
N
Member
Thread Starter
Join Date: May 2008
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Well I finally gave up and called a repair guy. The pilot generator wasn't putting out enough voltage and one the switches needed replacing. I had him replace all the switches and install a new generator everything is working fine now. Thanks for the help.