Hi everyone,
Winter is here and I've got an ice dam forming on the roof of a flat-top (low-incline) house. I just went to check the attic space and it seems cool, definitely not warm enough to melt snow. There is no insulation or ventilation. Could it be cool because the heat is running out the top? To add to the fun, the original shape of the home is a rectangle, but in the 1930s a triangle addition was put on the front (grey section), and the attic area of the addition is not accessible. Any help would be appreciated, I can't even seem to find information on whether or not ice dams are a real concern for flat, non-shingled roofs.
Winter is here and I've got an ice dam forming on the roof of a flat-top (low-incline) house. I just went to check the attic space and it seems cool, definitely not warm enough to melt snow. There is no insulation or ventilation. Could it be cool because the heat is running out the top? To add to the fun, the original shape of the home is a rectangle, but in the 1930s a triangle addition was put on the front (grey section), and the attic area of the addition is not accessible. Any help would be appreciated, I can't even seem to find information on whether or not ice dams are a real concern for flat, non-shingled roofs.
#2
Member
It sounds like the building has been around for awhile, so it must be holding it's own. But a couple of issues. First, any changes you make may affect more than the ice build up. For example, insulate that attic space real well, and the snow may build up instead of melding off, creating an increase in the snow load, thus potential structural problems. Simply shoveling off accumulated snow can be an answer.
Second, ice formation occurs at some unique combination of temperatures based upon the insulation, ventilation, the sun, and outside temperatures. Yes, ice dams are a concern for your building and all others as the accumulated weight of snow, ice, and water can exceed the building's load capacity.
I would start by gaining access to that closed off section of attic. Then look at options for insulating and venting, or sealing everything up with what is called a hot roof. A good place to start is with a couple of contractors providing recommendations and estimates. Any structural issues will usually go beyond a DIY project, so talking to a professional at the start just makes sense.
I've seen several low slope roof get totally replaced with pitched roofs and traditional attics, but I'm not sure what your budget is.
stay warm,
Bud
Second, ice formation occurs at some unique combination of temperatures based upon the insulation, ventilation, the sun, and outside temperatures. Yes, ice dams are a concern for your building and all others as the accumulated weight of snow, ice, and water can exceed the building's load capacity.
I would start by gaining access to that closed off section of attic. Then look at options for insulating and venting, or sealing everything up with what is called a hot roof. A good place to start is with a couple of contractors providing recommendations and estimates. Any structural issues will usually go beyond a DIY project, so talking to a professional at the start just makes sense.
I've seen several low slope roof get totally replaced with pitched roofs and traditional attics, but I'm not sure what your budget is.
stay warm,
Bud
#3
Member
Thread Starter
Join Date: Oct 2009
Location: Montreal
Posts: 35
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Hi Bud, thanks for the response.
Unfortunately it's a two-story home and the problem is on the second story. There's no way I'm going up there in the winter with a shovel.
That's what I was hoping to get on this forum.
But I know it's hard to say anything without seeing it in the flesh. The previous owners had set up a hot-wire across the length of the edge of the roof - perhaps a contractor recommended this. Unfortunately the only outdoor plug is ruined because it's right under an ice-cracked-leaky gutter. But that's another story.
Cheers,
Marc
Unfortunately it's a two-story home and the problem is on the second story. There's no way I'm going up there in the winter with a shovel.
A good place to start is with a couple of contractors providing recommendations and estimates. Any structural issues will usually go beyond a DIY project, so talking to a professional at the start just makes sense.

Cheers,
Marc
#4
Member
Glad to see you understand the view from here is limited. We always worry when giving advice, that the home owner will start cutting and building based upon our advice, which is often limited.
The general process of weatherizing takes into account attic heat, primarily because it carries moisture with it via the air leaks. So, your first stop is air sealing. Don't stop at what you thing are all of the air leaks, you will discover your home is a piece of swiss cheese, they all are. But sealing everything you can is the most cost effective of all improvements.
I hate hidden attics, you can't see problems early on to perhaps fix them before they come through the roof below.
I have a flat roof story for you. went to help a friend, almost flat roof with about 6" of ice at the eaves. It had been covered with rolled roofing, not shingles. Warm day so I was trying to dislodge the ice on the edge when a chunk let go. The flood of water behind it was astonishing. Had to be 50 plus gallons, but that rolled roof was holding up, no leaks. Tried to look into the attic, but previous owner had sheetrocked over the hatch. Wonder what he was hiding?
A picture might help. others will be by. http://forum.doityourself.com/electr...your-post.html
Bud
The general process of weatherizing takes into account attic heat, primarily because it carries moisture with it via the air leaks. So, your first stop is air sealing. Don't stop at what you thing are all of the air leaks, you will discover your home is a piece of swiss cheese, they all are. But sealing everything you can is the most cost effective of all improvements.
I hate hidden attics, you can't see problems early on to perhaps fix them before they come through the roof below.
I have a flat roof story for you. went to help a friend, almost flat roof with about 6" of ice at the eaves. It had been covered with rolled roofing, not shingles. Warm day so I was trying to dislodge the ice on the edge when a chunk let go. The flood of water behind it was astonishing. Had to be 50 plus gallons, but that rolled roof was holding up, no leaks. Tried to look into the attic, but previous owner had sheetrocked over the hatch. Wonder what he was hiding?

A picture might help. others will be by. http://forum.doityourself.com/electr...your-post.html
Bud
#5
Member
Thread Starter
Join Date: Oct 2009
Location: Montreal
Posts: 35
Upvotes: 0
Received 0 Upvotes
on
0 Posts
A few more detailed follow up questions:
1) Does the fact that the attic space is currently cool tell me anything about the temperature of the roof?
2) If I turn on the hotwire now after the dam + icicles have already formed, does this pose any danger? If the icicles fall, they'll go onto the first floor overhang, not someone's head, so that seems fine. The gutters below are already all frozen so I don't see it doing any more harm.
1) Does the fact that the attic space is currently cool tell me anything about the temperature of the roof?
2) If I turn on the hotwire now after the dam + icicles have already formed, does this pose any danger? If the icicles fall, they'll go onto the first floor overhang, not someone's head, so that seems fine. The gutters below are already all frozen so I don't see it doing any more harm.
#6
Member
A few more detailed follow up questions:
1) Does the fact that the attic space is currently cool tell me anything about the temperature of the roof?
2) If I turn on the hotwire now after the dam + icicles have already formed, does this pose any danger? If the icicles fall, they'll go onto the first floor overhang, not someone's head, so that seems fine. The gutters below are already all frozen so I don't see it doing any more harm.
1) Does the fact that the attic space is currently cool tell me anything about the temperature of the roof?
2) If I turn on the hotwire now after the dam + icicles have already formed, does this pose any danger? If the icicles fall, they'll go onto the first floor overhang, not someone's head, so that seems fine. The gutters below are already all frozen so I don't see it doing any more harm.
2. I've never used hotwires, but I would assume they are built to get wet and frozen into ice at times. You should be ok turning it on.
Bud