Leaking around vent or condensation underneath?


  #1  
Old 05-20-23, 10:32 AM
S
Member
Thread Starter
Join Date: Jun 2011
Location: USA
Posts: 44
Received 1 Upvote on 1 Post
Leaking around vent or condensation underneath?

Hope this is the right forum for posting:

Second floor bathroom exhaust fan roof vent. It's understandable that it's difficult to determine just by looking at photos but opinions would be much appreciated. Before damaged ceiling is replaced we need to determine if the bathroom exhaust roof vent is leaking from the roof side above or could this be years of condensation around the roof vent from the inside?

Photo #1: The damage is almost directly underneath the roof vent.

Photo #2: The square “adapter” attached to the roof has a 4” diameter galvanized extension to which the flexible duct is attached. The inner plastic sleeve section of the flexible duct was attached to the extension on the adapter with duct tape (a “no-no”) but was still secure. There wasn't any type of sealant used between the adapter and wood.

Photo #3: When I removed the adapter there didn't seem to be any staining or discoloration around the cutout for the roof vent. Also noticed that there wasn't any sealant used between the adapter and the roof.

For the record, roof is 17 years old. Roof vents for 1st and 2nd floor bath fan exhaust vents installed at same time. No other issues with leaks, even around our 1st floor bath fan exhaust.

Thanks in advance for any and all replies.





 
  #2  
Old 05-20-23, 12:46 PM
XSleeper's Avatar
Group Moderator
Join Date: Dec 2004
Posts: 26,406
Received 1,744 Upvotes on 1,568 Posts
Would need a photo from above. But its likely leaking from improper shingling around it.
 
Steverino voted this post useful.
  #3  
Old 05-20-23, 02:12 PM
S
Member
Thread Starter
Join Date: Jun 2011
Location: USA
Posts: 44
Received 1 Upvote on 1 Post
XSleeper: Getting up up the roof is my next step. Still recovering from attic venture.
 
  #4  
Old 05-20-23, 03:08 PM
XSleeper's Avatar
Group Moderator
Join Date: Dec 2004
Posts: 26,406
Received 1,744 Upvotes on 1,568 Posts
Ok, will keep an eye out for that. Your pipe wrap insulation should extend all the way to the roof. It's not unheard of for condensation (winter months) to run back down the pipe due to gravity... and damage the ceiling.

So if it's a winter leak, it's likely condensation, but could also be ice dam or similar. If its leaking when it rains, they probably lapped too many rows of shingles over it or just plain installed it poorly.
 
  #5  
Old 05-20-23, 09:52 PM
S
Member
Thread Starter
Join Date: Jun 2011
Location: USA
Posts: 44
Received 1 Upvote on 1 Post
XSleeper: The pipe wrap insulation was extended all the way to the roof prior to taking the photo. Just slid it down that far to check if the inner (plastic) sleeve was still attached and for the sake of the picture. Thinking back now, the insulation sleeve itself was a little loose at the very top. (Duct tape used there as well. Would be great if it were that simple.

Hoping to get on the roof Sunday and for a calm day. Glad the vent isn't too close to the edge of the roof. My wife's not crazy about me climbing around up there at my age. LOL

Thanks for keeping in touch.
 
  #6  
Old 05-21-23, 11:54 AM
S
Member
Thread Starter
Join Date: Jun 2011
Location: USA
Posts: 44
Received 1 Upvote on 1 Post
From up top

XSleeper: Might be too many pictures.

I can see a potential issue already with ice dams and possibly heavy rains over the years, especially if windy from the West. That cap has been up there for 17 years.

Bottom flange of vent cap pulled up. Aside from shingles closest to the vent cap which may have gotten pulled up a bit with the flange, all others seem ok. (Not a lapping issue?)

Could be a DIY fix? Roofing cement under flange and shingles nearby then secure with roofing nails; cover the new (and old) nails with sealer.

I was thinking LOCTITE PL Roof & Flashing 10-oz Black Paintable Polyurethane Caulk.

Your thoughts? And thanks for hanging in there with me. Much appreciated.



From backyard ground level




 
  #7  
Old 05-21-23, 12:10 PM
XSleeper's Avatar
Group Moderator
Join Date: Dec 2004
Posts: 26,406
Received 1,744 Upvotes on 1,568 Posts
I'd chisel or cut off the old caulk and recaulk it. Top and sides. You could also pull the 2 mails and replace them with neoprene and washer screws, and chase them with sealant. That means putting sealant on the threads of the screw once you get them started, then drive them in.
 
Steverino voted this post useful.
  #8  
Old 05-22-23, 07:26 AM
S
Member
Thread Starter
Join Date: Jun 2011
Location: USA
Posts: 44
Received 1 Upvote on 1 Post
XSleeper: Sounds like you're pretty much in agreement that the roof vent could have been the issue. Thank you again for your help.

Steverino
 
  #9  
Old 05-22-23, 07:40 AM
XSleeper's Avatar
Group Moderator
Join Date: Dec 2004
Posts: 26,406
Received 1,744 Upvotes on 1,568 Posts
Not necessarily. "Could be" but I don't see much evidence of leakage on the bottom of the roof deck. You'd usually have more staining there.

Lots of water can accumulate from condensation on a cold pipe in winter months after a hot shower. It runs down the INSIDE of the pipe and usually shows up right around the exhaust fan on the bathroom ceiling, or drips from a joint in the ductwork at an elbow.

All I'm saying is that it's prudent to caulk it. And if it was an ice dam that caused it, it could happen again.

The key piece of info is when did the leak first appear. Summer or winter?
 
  #10  
Old 05-22-23, 11:59 AM
S
Member
Thread Starter
Join Date: Jun 2011
Location: USA
Posts: 44
Received 1 Upvote on 1 Post
Understood. Initial plan is to seal up the vent cap as suggested.

As for the leak, it was eventually noticed over time as wavy areas in the ceiling almost directly under the roof vent. Winter or summer unknown. When the ceiling insulation was pulled up and I saw the sheet rock damage from the attic it felt on the damp side. Back in late March and early April of this year we had two torrential downpours and high winds.

I did pull the plastic cover off the bath exhaust at one time but couldn't tell if any water was running down inside the 4” duct.

Lots of work after sealing up vent cap on roof. New ceiling in bathroom followed by a new exhaust fan. Original exhaust in ceiling may have been a little too close to AC vent since I noticed a bit of staining around AV vent from attic. They were only about 14” apart.

Planning on R-8 insulated flex duct for the new fan. Will take my time to make sure all is secured with aluminum tape and well covered at the vent cap with the silver-faced insulation of the duct.

Thanks again!

Steverino


 
  #11  
Old 05-22-23, 12:42 PM
XSleeper's Avatar
Group Moderator
Join Date: Dec 2004
Posts: 26,406
Received 1,744 Upvotes on 1,568 Posts
Something I like to do with bath vents that go straight up is install a tee with a cap on the bottom as my elbow. And then mastic up the edges of that cap. That way any minor condensation will run straight down and hopefully harmlessly collect in the cap where it can evaporate.

Then bury your horizontal run to the bath fan with as much insulation as you reasonably can.
 
Steverino voted this post useful.
 