Search: Posts Made By: bobalua
Showing results 1 to 5 of 5
Search took 0.01 seconds.
Replies: 8
Views: 5,101
Posted By bobalua

It tripped because I adjusted the flame too high...

It tripped because I adjusted the flame too high when I was adjusting the flames on the burners. I have ordered a new roll out switch and did all inspections you suggested, I appreciate your concern....
Replies: 8
Views: 5,101
Posted By bobalua

Yea I found the safety switch for the burner,...

Yea I found the safety switch for the burner, jumpered it and voila I have fire. Now to order the safety switch. Thank You So Much NJ Trooper!!!!
Replies: 8
Views: 5,101
Posted By bobalua

I read B! & B3 to ground but when I measured...

I read B! & B3 to ground but when I measured between B1 and B# I got 23.6V. When I measured between TH and TR I got 0.0. So its either the safety switch on the burner or the damper safety switch is...
Replies: 8
Views: 5,101
Posted By bobalua

Slant/Fin Sentry Gas Fired Model S-120P; Gas...

Slant/Fin Sentry Gas Fired Model S-120P; Gas Valve Honeywell VR8200A2421 24 volt; Taco Low water cutoff LNA 1203S-1 (green light is on); Slant/Fin Damper part # 412706040 24volt; 4 zone switching...
Replies: 8
Views: 5,101
Posted By bobalua

Replacing Honeywell L8148E aquastat relay with L8148J1009

I am replacing an aquastat relay because my boiler would not fire, also there was no voltage at TV and T. On the new L8148J1009 it came with an additional jumper that goes from Z to TP. The...
Showing results 1 to 5 of 5


 