04-03-17, 01:54 PM
Replies: 9
Views: 1,469
Posted By ctransj

I replaced with a new motor that has the same...

I replaced with a new motor that has the same spec: RPM, AMP, 4 wires configuration and correct capacitor. I don't notice any reduce in the air flow from the vents. Unfortunately, when i realized...
03-25-17, 09:42 PM
Replies: 9
Views: 1,469
Posted By ctransj

Thanks all for the replies. I replaced the new...

Thanks all for the replies.
I replaced the new motor with the same spec so the air flow is pretty much the same. I also get warm air through the vents so the direction is good :).
I made a mistake...
03-23-17, 05:39 PM
Replies: 9
Views: 1,469
Posted By ctransj

Fan restarts after gas furnace turns off

After replacing the motor of my home furnace due to dried lubricant. I noticed a new strange behavior. After the furnace turns off, the fan just starts 10 seconds later for 1-3 minutes and turns off....