12-15-12, 04:37 PM
Replies: 11
Views: 2,263
Posted By SeattlePioneer

Measure tghe voltage at the LIM1 terminal on the...

Measure tghe voltage at the LIM1 terminal on the gas valve. You probably have 24 VAC there.

Check the voltage at LIM2. You probably have no voltage there.

If that's the case, check the...
12-15-12, 12:09 PM
Replies: 11
Views: 2,263
Posted By SeattlePioneer

There is no inducer motor on this gravity vented...

There is no inducer motor on this gravity vented furnace.

The fact that the fan is running suggests that the low voltage (24 VAC) power is not operating properly. Usually on these furnaces, you...