Replies: 28
Views: 2,369
Posted By PJmax

Good to see you finally back in operation. Thanks...

Good to see you finally back in operation. Thanks for stopping back and letting us know the outcome.
Replies: 28
Views: 2,369
Posted By PJmax

I don't think the cord is defective. I think it...

I don't think the cord is defective. I think it may be wired wrong. At least open the cover on the back and check.

The dryer worked up until the disconnect melted. The electrician rewires the...
Replies: 28
Views: 2,369
Posted By PJmax

If the problem you are having now with the...

If the problem you are having now with the breaker tripping after turning the dryer on only started after the electrician rewired the plug then you need to remove the cover where the power cord...
Replies: 28
Views: 2,369
Posted By PJmax

The electrician plugged the dryer in to the...

The electrician plugged the dryer in to the freshly rewired receptacle. When he turned the dryer on the breaker tripped. That sounds like a dryer problem.

Now you are saying that the breaker trips...
Replies: 28
Views: 2,369
Posted By PJmax

This was asked several times.... did you try it. ...

This was asked several times.... did you try it.

Normally an old disconnect is not used a junction box. In the upper left corner of the disconnect I see one white and two black wires coming in....
Replies: 28
Views: 2,369
Posted By PJmax

Regardless.... the Main should not trip before...

Regardless.... the Main should not trip before the 30A dryer breaker.