11-12-13, 08:58 PM
Replies: 8
Views: 1,046
Posted By brownsdog

Grady, That was it, thanks so much. I...

Grady, That was it, thanks so much.
I disconnected the pressure swith and it came right on.
I should have figured that was it but duh!
Thats why I came here, knew someone would have the answer.
I...
11-10-13, 07:30 PM
Replies: 8
Views: 1,046
Posted By brownsdog

Fired: As far as i can tell there was a call for...

Fired: As far as i can tell there was a call for heat then the led started flashing 2x

Grady: Thanks for the info, I will give that a shot tomarrow and see what happens.
11-10-13, 05:11 PM
Replies: 8
Views: 1,046
Posted By brownsdog

Yes, I checked the wies that connect to the vent...

Yes, I checked the wies that connect to the vent motor - no Power.
I cheched for continuity of the vent motor wires - good.
I checked for power at the connections on the board - no power.

What...
11-10-13, 03:08 PM
Replies: 8
Views: 1,046
Posted By brownsdog

No power to the Vent motor

I changed out the board, transformer, thermostat and checked all wiering 4 x

I even put the old board in a different unit and it worked fine!!!

I checked the continuity of the vent motor wires...