11-24-13, 09:04 AM
Replies: 9
Views: 3,621
Posted By Retarmy

Yes it was good, the circuit board came with many...

Yes it was good, the circuit board came with many different harnesses for if fervent applications, very nice. My furnace is working, with the temperatures outside below freezing. This is great.
11-23-13, 09:01 AM
Replies: 9
Views: 3,621
Posted By Retarmy

No I have a Honeywell S9200U1000, I needed it...

No I have a Honeywell S9200U1000, I needed it yesterday and the local Appliance parts distributor for the public only had one and that's what I'm using.

I would have preferred the Rodgers.
11-22-13, 11:57 PM
Replies: 9
Views: 3,621
Posted By Retarmy

I don't want to bypass any of the safety...

I don't want to bypass any of the safety switches, they're there for a reason. I'm glad I had to take some time to learn about the furnace.

I just didn't see the jumper on initial reading and...
11-22-13, 06:37 PM
Replies: 9
Views: 3,621
Posted By Retarmy

PJmax, I looked at the booklet again and the...

PJmax, I looked at the booklet again and the jumper was mentioned in a note. The (rollout ) switch is not on my Trane XB80 so it needs a jumper because the circuit board keeps looking for the rollout...
11-22-13, 11:14 AM
Replies: 9
Views: 3,621
Posted By Retarmy

I prayed about it and woke up this morning temp...

I prayed about it and woke up this morning temp in house was 59, I was about ready to call a tech in. I prayed some more and The Lord led me to re read the instructions. I was tracing every...
11-21-13, 11:49 PM
Replies: 9
Views: 3,621
Posted By Retarmy

Trane XB80 Heating issues

Replaced ignitor
Replaced flame sensor, needlessly
Issue: furnace will ignite and run maybe 15-20 minutes then shuts off, immediately tries to restart. The only thing flashing is fast flash calling...