11-23-16, 08:27 AM
Replies: 5
Views: 1,037
Posted By WiFiGuy

Heat's back on

OK, first off, thanks for the replies to the original post and for the comments.

Pete was right, the new pressure switch did not solve the problem it did, however, lead to the fix. Here's how:
...
11-22-16, 02:14 PM
Replies: 5
Views: 1,037
Posted By WiFiGuy

Thanks Pete

I'll put the new switch in and see what happens.

Before that, I'll check to see if the hole to the inducer motor is clogged.

I'll let you know how it goes.

Thanks again
11-22-16, 01:43 PM
Replies: 5
Views: 1,037
Posted By WiFiGuy

Gas furnace pressure switch question

Hi,

Our 4 year old Trane XB90 is not firing. It is showing a two-flash error light on it's board.

The problem started early Monday morning then went away when I vacuumed about two feet into...
06-04-16, 10:21 AM
Replies: 2
Views: 875
Posted By WiFiGuy

Bathroom Sink Cut Out Question

Hi,

We are remodeling our bathroom and are now ready to order our vanity counter top.

The vanity will be going into a corner of the room. So when we ordered it, the designer at HD included a...
02-08-16, 04:27 PM
Replies: 19
Views: 5,013
Posted By WiFiGuy

Thumbs up First off, I'd like to thank everyone who took...

First off, I'd like to thank everyone who took the time to post answers to my questions. From what I have read, it appears that each of you have raised some very valid points with regard to the "best...
02-07-16, 09:49 AM
Replies: 19
Views: 5,013
Posted By WiFiGuy

OK...excellent advice, thanks! I'll go with...

OK...excellent advice, thanks!

I'll go with the 1/2 inch plywood and will see about renting a stapler. I already have a compressor.

Will 3/4 inch staples do the job?
02-07-16, 08:42 AM
Replies: 19
Views: 5,013
Posted By WiFiGuy

forgot to ask...

Sorry, forgot to add this to the last post:

For the new plywood, should we screw it into the joists or can it get just screwed into the original plywood?
02-07-16, 08:32 AM
Replies: 19
Views: 5,013
Posted By WiFiGuy

Thanks...

Thanks for the quick replies and I see your point about adding another layer of plywood and then going with thinner cement board.

Makes perfect sense but are you sure about the 3/4 inch...
02-06-16, 01:10 PM
Replies: 19
Views: 5,013
Posted By WiFiGuy

Hardie Backer vs. Durock for bathroom floor backer

Hi,

I'm remodeling a bathroom. The tub is in, the tub surround is in (1/2" Durock) and we're now ready to prepare the floor for tile.

My questions:

Should I keep with Durock as the...
12-15-15, 08:48 AM
Replies: 9
Views: 1,808
Posted By WiFiGuy

OK, I followed Ray's suggestion and picked up a...

OK, I followed Ray's suggestion and picked up a piece of 3 inch ABS pipe from the RV store.

Dry fitted it into the existing Wye fitting and it goes in with no problem. It fits fairly snuggly,...
12-04-15, 02:37 PM
Replies: 9
Views: 1,808
Posted By WiFiGuy

Thanks Ray

Called around this AM and found that no one carries ABS in stock. The only way I can get what I need would be to order a 20 ft. pipe--and that's about 19 more feet than I need.

At Ray's...
12-04-15, 10:13 AM
Replies: 9
Views: 1,808
Posted By WiFiGuy

Thanks Carbide

Thanks for the advice Carbide, it sounds like it should work as long as I can make a good connection inside the elbow. The inside of the elbow's hub is in pretty good shape. I used a heat gun to get...
12-04-15, 07:41 AM
Replies: 9
Views: 1,808
Posted By WiFiGuy

ABS Water Closet Flange Question

Hi,

We're renovating a 70s-built bathroom and have removed the tub, toilet, wall tiles and tile (mud job) floor.

Since the toilet flange was not in good shape it came out as well. The drain...
11-30-11, 09:12 AM
Replies: 16
Views: 13,399
Posted By WiFiGuy

Circulation Fan is the problem

Over the weekend I got the circulation fan working by spinning it by hand a few times. It came on OK but did make a noise that sounds like it may have a bad bearing in it. With the fan working, the...
11-25-11, 12:59 PM
Replies: 16
Views: 13,399
Posted By WiFiGuy

Going to call a repair guy on Monday

I hooked up the multi meter and checked the voltage coming from the primary control to the motor it read 120V when I started the furnace.

Since it hard to tell for sure if the motor is running...
11-25-11, 10:28 AM
Replies: 16
Views: 13,399
Posted By WiFiGuy

Fan Limit Control shutting down burner

I just checked the fan limit control and it is indeed shutting down the burner. As the burner runs, the blower is not coming on so the heat is staying in the furnace causing the fan limiter control...
11-25-11, 08:27 AM
Replies: 16
Views: 13,399
Posted By WiFiGuy

Make and Model

I'm still looking for the manual, but not having too much luck.

Here is the make and model of the furnace:

Ruud / Rheem Highboy Model U0BB-112C-JA

Thanks
11-24-11, 10:58 AM
Replies: 16
Views: 13,399
Posted By WiFiGuy

Overheating sounds about right

Thanks Grady, it does appear to get pretty hot just prior to shut down. Therefore, a fan control issue does make perfect sense. I'll try to locate the manual for the furnace, maybe it will have a...
11-23-11, 04:19 PM
Replies: 16
Views: 13,399
Posted By WiFiGuy

Here's the latest: The new breaker appears...

Here's the latest:

The new breaker appears to have solved the breaker tripping problem. It tripped once right after I put it in but hasn't since.

Here's where things stand now:

When the...
11-21-11, 12:59 PM
Replies: 16
Views: 13,399
Posted By WiFiGuy

Maybe a bad relay

After putting the motor back in and disconnecting the humidifier and water pump, I re-started the furnace and it did the same as before--fired up ran for about 30 seconds and then shut off due to the...
11-21-11, 11:11 AM
Replies: 16
Views: 13,399
Posted By WiFiGuy

Or maybe the breaker is bad?

Or maybe the breaker is bad?
11-21-11, 11:03 AM
Replies: 16
Views: 13,399
Posted By WiFiGuy

Blower motor is good

I took off the blower motor and plugged it into an AC outlet and it worked fine. I let it run for a few minutes and it didn't trip any breakers.

Could the problem be the relay switch or the...
11-21-11, 07:56 AM
Replies: 16
Views: 13,399
Posted By WiFiGuy

It's the breaker on the panel that it tripping. ...

It's the breaker on the panel that it tripping.

Thanks
11-20-11, 12:57 PM
Replies: 16
Views: 13,399
Posted By WiFiGuy

Blower Motor P/N

Here is the replacement motor, mine is a P/N 2456 cost = $45 on-line:

BECKETT BURNER MOTOR FOR MODELS AF, AFG and NX 1/7 HP, 3450 RPM, 120 vac, PSC (Permanent Split Capacitor), FRAME 48M, lower...
11-20-11, 09:34 AM
Replies: 16
Views: 13,399
Posted By WiFiGuy

Oil burner tripping breaker

Hi,

We have an oil furnace that has a Beckett AF oil burner. A week or so ago when we didn't have heat we noticed that its breaker was tripped. After resetting the breaker, it came on and ran...