11-23-14, 09:27 AM
Replies: 9
Views: 3,864
Posted By Ohio_Guy

Looked at it a little more. Some of the holes in...

Looked at it a little more. Some of the holes in the existing neutral/ground bus bar are small, and some are large. The panel says the large holes can accommodate #6 stranded.

The existing...
11-23-14, 08:19 AM
Replies: 9
Views: 3,864
Posted By Ohio_Guy

Am I'm not sure why there are so many neutrals....

Am I'm not sure why there are so many neutrals. Will look into this, too.

While I'm at it... what's the rule on "doubling up"? Am I allowed to have two ground wires in the same slot? Am I allowed...
11-23-14, 08:16 AM
Replies: 9
Views: 3,864
Posted By Ohio_Guy

Thanks for the feedback. Yea, that's grease...

Thanks for the feedback.

Yea, that's grease on the aluminum neutral conductor coming from the meter.

I never thought that a #6 would be able to fit into one of the small lugs in the existing...
11-23-14, 07:45 AM
Replies: 9
Views: 3,864
Posted By Ohio_Guy

Circuit breaker panel problem

Our house has a 200 A main panel. It's a General Electric panel that was installed in 1989, when the house was built.

I am in the process of installing a 120/240 V, 50 A receptacle in the...