No typo, there’s 2 blacks (hots going to the...

No typo, there’s 2 blacks (hots going to the supply), 2 whites (going to a buss bar on the left), and a green ground going to a bar on the right. I wish I know how to post a pic on here lol.
05-07-19, 02:45 PM
Replies: 13
Views: 1,944
Posted By cliftonjc20

It was a hope inspector. He stated on the report...

It was a hope inspector. He stated on the report that the breaker was oversized. 50amp breaker with 8awg.
05-07-19, 01:15 PM
Replies: 13
Views: 1,944
Posted By cliftonjc20

Would I be able use 6/3 romex (in conduit)...

Would I be able use 6/3 romex (in conduit) instead of the 8 awg THHN
05-07-19, 09:17 AM
Replies: 13
Views: 1,944
Posted By cliftonjc20

Sub panel wire size questions.

I bought a house and the inspector tagged the wiring to the sub panel in the attached garage.

The main box (200 amp) is on the back of the house and conduit runs from a 50amp breaker from the...