02-07-11, 02:41 PM
Replies: 11
Views: 16,629
Posted By mjohnsn

Final Call

FYI. LP conversion kit was included in install. Gas line pressure was not the problem.

Hvactechfw nailed it. Replaced controller and everything toasty again.

Thanks to all.
02-06-11, 08:04 PM
Replies: 11
Views: 16,629
Posted By mjohnsn

Gas pressure appears to be good. Range runs off...

Gas pressure appears to be good. Range runs off the same line and burners are at full power.
Can not hear or smell gas when gas valve is energized. Now notice that igniter only cycles twice. ...
02-06-11, 03:59 PM
Replies: 11
Views: 16,629
Posted By mjohnsn

Gas control manual switch is on. Cut off valve to...

Gas control manual switch is on. Cut off valve to unit is open. Propane tank is filled to top. Gas control valve is new unit. HSI heats up normally. Controller throws 24 VAC to energize gas valve...
02-06-11, 01:50 PM
Replies: 11
Views: 16,629
Posted By mjohnsn

chain of events

Will try to make it clearer. When thermostat makes a call for heat, the blower (in the same compartment as the burners) starts to blow. Shortly after that the hot surface igniter starts to glow....
02-06-11, 12:10 PM
Replies: 11
Views: 16,629
Posted By mjohnsn

Heil furnace continuous fan, no heat, ignition problem?

Have a Heil hot surface ignition gas furnace which first presented continuous fan no heat. After shutdown and kinetic repair of fan limit timing switch it started back up.
Became progressively...