I think they may have wired the neutrals together...

I think they may have wired the neutrals together at the back or front porch switch. I don't know if it was accidental or intentional but would the neutral account for all the outlets having no...
12-05-19, 12:10 PM
Replies: 6
Views: 472
Posted By backstabber

It's two separate MWBC's. A 15a for lights (red,...

It's two separate MWBC's. A 15a for lights (red, black) and a 20a for outlets (red, black).

12-04-19, 06:20 PM
Replies: 6
Views: 472
Posted By backstabber

Dead outlets with .4 volts

So I have outlets and lights on a mwbc. A 15a dp feeds the lights and a 20a dp feeds the outlets. If I turn off both dp breakers, I get no voltage (obviously) but if I switch both on, the lights...