10-02-19, 09:23 AM
Replies: 15
Views: 502
Posted By 62Galaxie

Allanj, I had not thought about putting all...

Allanj,

I had not thought about putting all three on the 30 amp breaker that way, but it will work. The 9.0 amp heater is in a porch and we only keep it at 60 degrees and it doesn't run a lot...
10-02-19, 07:06 AM
Replies: 15
Views: 502
Posted By 62Galaxie

AllanJ, That's the way I'm going to wire...

AllanJ,

That's the way I'm going to wire them. I think I have a box and breakers at home even. The 6.3 amp heater can be wired to another heater circuit.

Zorfdt,

I'll have to check the...
10-01-19, 09:49 AM
Replies: 15
Views: 502
Posted By 62Galaxie

Zorfdt, These are 240 volt heaters. I'm...

Zorfdt,

These are 240 volt heaters. I'm unfamiliar with using a relay on the thermostat to control two heaters. Can you explain this more or a link that I can look at?

Thanks,
Bob
10-01-19, 09:15 AM
Replies: 15
Views: 502
Posted By 62Galaxie

Joed, Whay would I need 10/3 wire? I...

Joed,

Whay would I need 10/3 wire?

I thought about using the 30 amp cirucuit and then a sub panel with 15 amp breakers for the 9.0 and 8.3 amp heaters. And then adding the 6.3 amp heat onto a...
09-30-19, 08:42 PM
Replies: 15
Views: 502
Posted By 62Galaxie

Thanks PjMax. I forgot about the 80% rule. ...

Thanks PjMax.

I forgot about the 80% rule. I'm going to have figure out another way to do this.

Bob
09-30-19, 07:56 PM
Replies: 15
Views: 502
Posted By 62Galaxie

That was one of my concerns. I didn't see...

That was one of my concerns. I didn't see anything on the heaters about the circuit size. So, can I put the 9.0 amp and 8.3 amp on a 20 amp breaker or will the startup amps of both be too much for...
09-30-19, 07:43 PM
Replies: 15
Views: 502
Posted By 62Galaxie

Can I put 3 electric wall heaters on same ciruit?

I have 3 electric wall heaters that I need to run power to. Here's the amps for each heater 8.3, 9.0, and 6.3. I have a 30 amp breaker available with #10 wire already wired to the 8.3 amp breaker. ...
01-26-12, 08:24 AM
Replies: 2
Views: 2,737
Posted By 62Galaxie

Furnace exhaust pipe running through insulation?

We bought a house on foreclosure that thas a natural gas water heater and furnace. The exhaust piping for both is PVC. Both are in the basement and the basement was dug after the house was built, so...
Forum: Water Heaters
01-26-12, 08:19 AM
Replies: 6
Views: 1,371
Posted By 62Galaxie

Rust in water heat?

We bought a house that has sat empty for two years, it was a foreclosure house. There was some frozen water lines so I repaired them and put the gas water heater back in place and turned the water...