11-07-10, 03:04 PM
Replies: 10
Views: 7,920
Posted By IBStramezi

Maybe I'll be able to find a heating contractor...

Maybe I'll be able to find a heating contractor that can bench test my circuit board.
11-07-10, 01:40 PM
Replies: 10
Views: 7,920
Posted By IBStramezi

Yes, that is exactly what I thought, that, if it...

Yes, that is exactly what I thought, that, if it comes to it, it's probably cheaper to put in a new board than call in a serviceman. The one wildcard in all this is that I vacuumed the furnace...
11-07-10, 01:01 PM
Replies: 10
Views: 7,920
Posted By IBStramezi

Hope I did this right: I jumpered R and W1 and...

Hope I did this right: I jumpered R and W1 and the furnace immediately tried to fire, but failed. Then jumpered R and W2 and got the same results I have been all along. I also tried disconnecting the...
11-07-10, 12:34 PM
Replies: 10
Views: 7,920
Posted By IBStramezi

The draft inducer motor also quits immediately....

The draft inducer motor also quits immediately. If I turn down the thermostat, turn on the furnace and then raise the thermostat, I get the same failed sequence. I don't see any indication of loose...
11-07-10, 11:27 AM
Replies: 10
Views: 7,920
Posted By IBStramezi

Yes, the draft fan comes on when the hearbeat...

Yes, the draft fan comes on when the hearbeat speeds up. The ignitor and gas valve both get energized for a fraction of a second, but not long enough enough for ignition-no glow and no gas, that I...
11-06-10, 07:24 PM
Replies: 10
Views: 7,920
Posted By IBStramezi

Trane XV80 won't start

Trane XV80 gas furnace, 9 years old.

~30 second initialization with red LED flashing slowly.

Then red LED flashes fast and duct fans come on. Ignitor is energized with 115V for about a half...