06-13-08, 08:53 PM
Replies: 7
Views: 5,614
Posted By vctaillon

it tuns out....:)

that the neutral wire at the panel was very loose. The screw was backed out all the way for this particular circuit. All's well now. Thanks for your advice on this!
06-10-08, 03:27 AM
Replies: 7
Views: 5,614
Posted By vctaillon

funny thing is...

funny thing is the voltage tester, indicates 115-120v from black to ground, but still open neutral
06-09-08, 08:01 PM
Replies: 7
Views: 5,614
Posted By vctaillon

open neutral continued

this is a home (older 1960's) with upgraded electric breaker box. The previous owners were in the process of upgrading however not all recpts have been replaced yet.

On this circuit, there are 3...
06-09-08, 04:18 PM
Replies: 7
Views: 5,614
Posted By vctaillon

open neutral?

there are 3 recepticles in our kitchen that "trip off" by themselves. the circuit breaker in the main bus stays on. I put a circuit tester on them, and the lamps indicate that there is an open...
06-05-08, 06:21 PM
Replies: 11
Views: 2,119
Posted By vctaillon

thanks for feedback

It's been about a week and the power in the kitchen has remained on. It does look like there is too much on this one circuit. We will have to split it up and add more 15 amp circuits.
06-01-08, 04:51 PM
Replies: 11
Views: 2,119
Posted By vctaillon

The house is 45 years old............

The house is 45 years old, most of the original wire is aluminum. if the breaker breaks half way, what does that indicate?
06-01-08, 04:47 PM
Replies: 11
Views: 2,119
Posted By vctaillon

The GFI's are on the same circuit and no they...

The GFI's are on the same circuit and no they don't trip. Nothing trips. The circuit breaker looks normal in the main box. Simply we are in the kitchen, and the power goes and off goes the fridge....
06-01-08, 04:42 PM
Replies: 11
Views: 2,119
Posted By vctaillon

I have isolated which circuit it is........

I have isolated which circuit it is. I know it's not tripped because it's not orange, however when I reset it the power comes back on. I've heard pops or clicks sometimes at the main board. Like I...
06-01-08, 01:21 PM
Replies: 11
Views: 2,119
Posted By vctaillon

Question 15 amp breaker trips without breaking

Hi,
We seem to have a electrical issue in our kitchen. Our fridge is on a 15 amp circuit with 5 counter recepticles and also 2 recepticles in the basement (one which feeds a sump pump) and 2...