11-05-11, 10:55 AM
Replies: 9
Views: 9,360
Posted By tkattre

Thats what I will try thanks so much for your help

Thats what I will try thanks so much for your help
11-05-11, 08:12 AM
Replies: 9
Views: 9,360
Posted By tkattre

Yes when I checked the pv wire I see 30vac then...

Yes when I checked the pv wire I see 30vac then the relay kicks in the mv wire only gets to 10vac which isnt high enough to trip the relay I also disconnected the gas and put 24vac on the mv wire and...
11-04-11, 01:05 PM
Replies: 9
Views: 9,360
Posted By tkattre

I will check that tonight when I get home. I am...

I will check that tonight when I get home. I am in electronics and have access to external power supplys. Do you think if I inject 24v on the mv wire when the pilot comes on that the main burners...
11-04-11, 11:46 AM
Replies: 9
Views: 9,360
Posted By tkattre

Sorry but to answer your question there is only 1...

Sorry but to answer your question there is only 1 flame sensor and it is part of an assembly with the pilot light attached to it
11-04-11, 10:04 AM
Replies: 9
Views: 9,360
Posted By tkattre

You are correct it is a honeywell the spark stays...

You are correct it is a honeywell the spark stays on and the pilot comes on the spark shuts off. the main burners never come on and the pilot shuts off after 3 seconds or so. then the whole process...
11-04-11, 06:47 AM
Replies: 9
Views: 9,360
Posted By tkattre

Heil furnace problem

I have an older heil furnace model NUGI075DF03 The pilot light lights for about 3 seconds then shuts off the main burners dont light. This process will keep repeating itself. Question is how do I...