06-25-19, 05:20 AM
Replies: 16
Views: 821
Posted By ibpooks

To wire that compressor on 240V, you would want...

To wire that compressor on 240V, you would want to change out the breaker for a 2-pole 20A breaker and use 12-2 cable. Eaton makes exact replacements for Westinghouse/Bryant breakers so you should...
06-24-19, 03:01 PM
Replies: 16
Views: 821
Posted By PJmax

This would be a mistake or an error in wiring. A...

This would be a mistake or an error in wiring. A standard receptacle circuit cannot be protected over 20A.

Running that compressor on 240v would be a smart choice. That means you will need an...
06-23-19, 05:43 PM
Replies: 16
Views: 821
Posted By joed

You can not rely on the colour of the NM cable to...

You can not rely on the colour of the NM cable to indicate the gauge. It used to all be white. Check the actual cable gauge. Either measure it or check the cable casing. It will be stamped on it.
...