Replies: 11
Views: 2,746
Posted By SOHIO

Just found out my Honeywell 8148A aquastat is not...

Just found out my Honeywell 8148A aquastat is not turning the Taco 007 pump on!

No voltage C1-C2 when call for heat, zones open up.
Burner fires and shuts off when supposed to.
Jumped L1 to C1...
Replies: 11
Views: 2,746
Posted By SOHIO

The oil boiler is a Burnham V714 rated @ 113MBH...

The oil boiler is a Burnham V714 rated @ 113MBH [BTU]
Manual;Burnham V7 SERIES free Manual (Page 8) (http://www.manualslib.com/manual/23109/Burnham-V7-Series.html?page=8#manual)
Honeywell 8148A...
Replies: 11
Views: 2,746
Posted By SOHIO

Thank you for the response! Ok, I think I'm...

Thank you for the response!

Ok, I think I'm going to do the wrap-a-round set up.
Instead of hacking the existing pipes I'm going to pipe it using the other ports that are in the boiler, and they...
Replies: 11
Views: 2,746
Posted By SOHIO

Portage and main manual has a three way valve.[...

Portage and main manual has a three way valve.[ pg 13 ]
http://woodheating.ca/p+m_furnace_man.pdf

This one has a pump on the supply side [new style of hydronic recommendations ] mine has it on...
Replies: 11
Views: 2,746
Posted By SOHIO

? on hooking up OWB to HX to existing oil boiler

I just installed a Portage and Main ML36 outside wood burner. I have an existing oil boiler that I want to use as a back up source. I have a 50 plate heat exchanger that will seperate the two...