09-15-07, 05:06 PM
Replies: 6
Views: 2,147
Posted By marcerrin

Replace the cord with a 4-prong cord.

Replace the cord with a 4-prong cord.
Replies: 3
Views: 762
Posted By marcerrin

Was the dimmer installed a 3-way dimmer? If not,...

Was the dimmer installed a 3-way dimmer? If not, that would cause the problem your describing. If it is a 3-way dimmer, its installed wrong.
04-28-07, 09:38 PM
Replies: 9
Views: 1,133
Posted By marcerrin

Its a feeder, #4 would work for 100amp. #2 would...

Its a feeder, #4 would work for 100amp. #2 would be 125amp.
04-28-07, 09:29 PM
Replies: 15
Views: 1,525
Posted By marcerrin

yes. Dont forget to run an insulated #8 green...

yes. Dont forget to run an insulated #8 green wire in the pipe along with the factory cord. There will be a ground lug inside the case of the wet niche fixture to land this #8 on. Also, you'll need a...
04-14-07, 07:20 PM
Replies: 3
Views: 1,012
Posted By marcerrin

Washington State requires a dedicated circuit for...

Washington State requires a dedicated circuit for the diswasher.
Replies: 2
Views: 1,322
Posted By marcerrin

Kenmore 90 series dryer.

I get an electrical buzzing noise when trying to start the dryer. Sometimes it will slowly start up and then turn itself off in a couple minutes, or it will just stop buzzing till i let it sit for a...
Replies: 2
Views: 826
Posted By marcerrin

'85 ford f250

I was wondering how hard/expensive it is to change the tranny from a manual to an automatic. It has a 351 windsor, with a manual transmission. Is this something I can attempt on my own? Or should I...
07-25-03, 05:23 PM
Replies: 4
Views: 968
Posted By marcerrin

Intermatic WP1010, thats what i use.

Intermatic WP1010, thats what i use.
06-04-03, 07:42 PM
Replies: 1
Views: 1,043
Posted By marcerrin

You could try one of these....

You could try one of these. http://www.x10.com/automation/x10_lm15a.htm
06-04-03, 07:30 PM
Replies: 1
Views: 1,422
Posted By marcerrin

Youve hooked it up wrong and the chime solinoid...

Youve hooked it up wrong and the chime solinoid is stuck in the closed position as if your button is being held down. Tell us what wires you hooked up where.
05-30-03, 09:13 PM
Replies: 2
Views: 1,175
Posted By marcerrin

Through a hole? Or through the entire joist bay?

Through a hole? Or through the entire joist bay?
05-30-03, 09:10 PM
Replies: 2
Views: 925
Posted By marcerrin

When your looking on the inside of the fixture it...

When your looking on the inside of the fixture it gives a max wattage for the trim style. If this is in a shower, Im going to assume that this is a sealed trim, and I believe in most cans the max...
05-30-03, 09:03 PM
Replies: 7
Views: 8,045
Posted By marcerrin

In order to use the "ufer" ground method, you...

In order to use the "ufer" ground method, you have to prove that the rebar is, or is connected to at least 20 linear feet of buried rebar.
250.52(a)(3)
05-30-03, 08:55 PM
Replies: 27
Views: 2,137
Posted By marcerrin

I concur with John on the 2" pipe, it cant hurt....

I concur with John on the 2" pipe, it cant hurt. It will also make the pull a breeze.
05-22-03, 11:21 PM
Replies: 2
Views: 2,524
Posted By marcerrin

I go 80" from rough floor, unless its spec'd...

I go 80" from rough floor, unless its spec'd otherwise. Havent had any problems.
05-22-03, 11:14 PM
Replies: 10
Views: 12,713
Posted By marcerrin

Sounds like a remodel can to me. Take it out, go...

Sounds like a remodel can to me. Take it out, go to HD and buy a new one for I think like $15 and replace the whole thing.
05-22-03, 11:01 PM
Replies: 2
Views: 1,679
Posted By marcerrin

No you dont have to bond the rebar, unless any...

No you dont have to bond the rebar, unless any part of it is exposed. Ive had inspectors make me bond window frames before, but its up to the local AHJ. No, your flex cannot be longer than 6', and it...
05-19-03, 10:54 PM
Replies: 1
Views: 781
Posted By marcerrin

A 12 or 24 volt ice cube relay. It should be...

A 12 or 24 volt ice cube relay. It should be available at any local electrical supply house.
05-18-03, 12:12 PM
Replies: 14
Views: 6,989
Posted By marcerrin

Posted by John Nelson

Posted by John Nelson
05-17-03, 12:28 AM
Replies: 14
Views: 6,989
Posted By marcerrin

Article 210.12 is where youll want to look. Did...

Article 210.12 is where youll want to look.
Did you connect the load neutral to the neutral lug on the breaker?
05-15-03, 08:34 PM
Replies: 5
Views: 9,385
Posted By marcerrin

Are you sure its the xformer buzzing and not the...

Are you sure its the xformer buzzing and not the bulbs? If I remember correctly Hampton Bay fixtures typically come with bulbs, cheap ones. Cheap bulbs are a common culprit to buzzing as well.
05-15-03, 08:17 PM
Replies: 5
Views: 9,385
Posted By marcerrin

Is the dimmer a low voltage dimmer? Or a line...

Is the dimmer a low voltage dimmer? Or a line voltage dimmer? For this application you need a magnetic low voltage dimmer.


But, there are some dimmers designed to dim transformers.
05-15-03, 01:36 AM
Replies: 1
Views: 709
Posted By marcerrin

It should be marked on the sheathing. If its not,...

It should be marked on the sheathing. If its not, you have to take it at 60.
05-15-03, 01:34 AM
Replies: 17
Views: 1,263
Posted By marcerrin

Dont forget this is a DIY forum. Yes, Im sure you...

Dont forget this is a DIY forum. Yes, Im sure you would check for proper bonding, but if you didnt know to, you wouldnt.


Do you disagree with my interpretation given earlier in my first post?...
05-14-03, 10:09 AM
Replies: 1
Views: 1,017
Posted By marcerrin

I dont think they specify in the code book, as...

I dont think they specify in the code book, as long as its clamped.