03-20-16, 04:46 PM
Replies: 8
Views: 742
Posted By Timmer62

Pete and Bob, thanks for the guidance. Time to...

Pete and Bob, thanks for the guidance. Time to call the pros. Now off to our leaky washing machine.
03-20-16, 02:12 PM
Replies: 8
Views: 742
Posted By Timmer62

By the way, switch not resettable, so perhaps...

By the way, switch not resettable, so perhaps indicator of low refrigerant. Switch part number is Texas Instruments 20ps08-0018.
03-20-16, 02:09 PM
Replies: 8
Views: 742
Posted By Timmer62

Pete, you called it. Pressure switch is locking...

Pete, you called it. Pressure switch is locking out the contactor. Did not know there was a pressure switch until now. As best I can tell, switch can't be removed without releasing refrigerant. ...
03-19-16, 03:20 PM
Replies: 8
Views: 742
Posted By Timmer62

I agree, but 3amp fuse survived the brief...

I agree, but 3amp fuse survived the brief experiments. Question is why is the low side coil terminal also at 24vac? Any ideas.
03-19-16, 02:28 PM
Replies: 8
Views: 742
Posted By Timmer62

A/C condenser issues.

I'm stuck. Neither condenser fan or compressor will turn on. Voltage across low voltage line (measured at wire nuts just inside condenser panel) is 24VAC. Voltage across L1/L2 at contactor is...