02-16-13, 04:42 AM
Replies: 15
Views: 1,745
Posted By kiyolaka

Yeah, atleast its not an urgent matter now. I...

Yeah, atleast its not an urgent matter now.
I vaccumed out the stack
+ bottom of chimney. What sort of brush would one use?
02-15-13, 07:36 PM
Replies: 15
Views: 1,745
Posted By kiyolaka

stack control was toast, replaced and have not...

stack control was toast, replaced and have not had an issue since.

also appearantly with this particular furnace being a one of a kind bottom vortex burner design, it has a bit of a unique gaping...
02-13-13, 05:31 PM
Replies: 15
Views: 1,745
Posted By kiyolaka

I gave up and have a pro coming to look at it on...

I gave up and have a pro coming to look at it on Friday. If I spend much more time with it I am likely to snap and rage on it.
02-13-13, 12:39 PM
Replies: 15
Views: 1,745
Posted By kiyolaka

Psi is approx 97 when I last checked. I've bled...

Psi is approx 97 when I last checked. I've bled the system quite a bit at the pump as well as at the filter. as well as replaced the tubing between the pump and nozzle (old flare had small crack in...
02-12-13, 09:41 PM
Replies: 15
Views: 1,745
Posted By kiyolaka

Yes, I do electronics repair as a bit of a...

Yes, I do electronics repair as a bit of a hobby/cheap way to fix stuff and get it for my house.
I also happen to own a cheap Endoscope.

before we go too much further could a restricted/failing...
02-11-13, 11:29 PM
Replies: 15
Views: 1,745
Posted By kiyolaka

I should probably note that this furnace fires...

I should probably note that this furnace fires oil upwards out of the bottom of the chamber as upposed to the burner itself.
I adjusted the electrodes so they are 1/16 (also tried 1/8) above the...
02-10-13, 11:58 PM
Replies: 15
Views: 1,745
Posted By kiyolaka

the burner is a bottom firing. the electrodes are...

the burner is a bottom firing. the electrodes are about 3/8 away from the nozle, 1/8 above it , and about 1/8 gap currently.

I have been suspicious of the heat ex changer given the furnace...
02-09-13, 11:15 PM
Replies: 15
Views: 1,745
Posted By kiyolaka

furnace keeps shutting down mid cycle - electrodes appear sooted

heres an older pic I took of the electrodes inside. I've since re-adjusted them a bit so they sit higher90929091

I question the condition of them, as well as the curve in their tip, all of the...