02-11-19, 03:12 PM
Replies: 48
Views: 1,232
Posted By AllanJ

Run the #4 ground wire to the neutral bar in the ...

Run the #4 ground wire to the neutral bar in the first panel in or on the building (the main panel here).
02-11-19, 07:04 AM
Replies: 48
Views: 1,232
Posted By AllanJ

Any kind of #4 copper wire can be used -- soft...

Any kind of #4 copper wire can be used -- soft drawn, oxygenated, stranded, solid, bare, tempered, insulated, etc. as available.
02-10-19, 06:05 AM
Replies: 48
Views: 1,232
Posted By AllanJ

The second Verizon box should have a ground wire....

The second Verizon box should have a ground wire. This ground wire can be attached anywhere along the ground wire going from the panel to the first Verizon box or anywhere along the #4 ground wire to...
02-09-19, 08:22 PM
Replies: 48
Views: 1,232
Posted By AllanJ

Can you verify that the small wire from the water...

Can you verify that the small wire from the water meter and going outside actually goes to some box or gadget outside that might be a sensor for meter reading?

A few days delay in completing the...
02-09-19, 06:25 AM
Replies: 48
Views: 1,232
Posted By AllanJ

When removing the "front" clamp from the copper...

When removing the "front" clamp from the copper pipe to be removed and replaced from the house side of the meter, do not cut any of the ground wires immediately. Rejoin any wire ends that came loose...
02-08-19, 06:12 PM
Replies: 48
Views: 1,232
Posted By AllanJ

Which copper pipe are you removing next?

Which copper pipe are you removing next?
02-07-19, 07:34 AM
Replies: 48
Views: 1,232
Posted By AllanJ

Where do the ground wires going outside go to? ...

Where do the ground wires going outside go to?
You cannot assume. You have to find out. This is the only way the problem can be solved with a minimum of new components added.

As things stand now...
02-06-19, 10:30 AM
Replies: 48
Views: 1,232
Posted By AllanJ

Nowadays the correct grounding electrode...

Nowadays the correct grounding electrode conductor runs from the main water line before the meter. In your case you have about eleven inches worth of eligible length of pipe to clamp the GEC to.
...