10-16-13, 08:10 PM
Replies: 11
Views: 1,867
Posted By Grady

Delayed ignition is the failure of the burner to...

Delayed ignition is the failure of the burner to ignite as soon as the motor starts. Unless your burner has been modified, the flame should appear within a fraction of a second of the motor starting.
10-16-13, 04:29 PM
Replies: 11
Views: 1,867
Posted By Grady

If it's been working that way for 20+ years, I...

If it's been working that way for 20+ years, I wouldn't monkey with it. Sorry I don't understand "groaning". Is there delayed ignition? If so, it could be the ignition transformer getting weak.
10-15-13, 09:29 PM
Replies: 11
Views: 1,867
Posted By Grady

That boiler should have an F6 burner head, a...

That boiler should have an F6 burner head, a 2.75" static plate, the pump pressure should be set at 100#, & the specified nozzle is a 1.25 x 80* B Delavan. You need to check the static plate, burner...
10-15-13, 08:29 PM
Replies: 11
Views: 1,867
Posted By Grady

It's not unusual to downfire a boiler but from...

It's not unusual to downfire a boiler but from 1.25 to .75gph is quite a drop. Often downfiring is done because of a lack of draft or due to short cycling. What model is the boiler (366,466, etc.)?
10-14-13, 03:41 PM
Replies: 11
Views: 1,867
Posted By Grady

You can just remove the burner. In general the...

You can just remove the burner. In general the chamber doesn't need to be vacuumed every year. Normally every 5 years or so is fine unless you get a lot of debris in there. When you do vacuum it out,...
10-07-13, 06:22 PM
Replies: 11
Views: 1,867
Posted By Grady

Chamber kits are readily available for that...

Chamber kits are readily available for that boiler & only take an hour or two to install. I wouldn't fire it without the chamber.